Sávio Pereira Posted June 17, 2019 Report Posted June 17, 2019 I want to replace a Micrologix 1500 whit a Unistream, but it there is a huge amount of IO cards. May I somehow use the 1764 family I/O expansion rack whit the Unistream? Could I use the Micrologix 1500 as a Slave for this?
MVP 2023 Joe Tauser Posted June 18, 2019 MVP 2023 Report Posted June 18, 2019 If you have a good understanding of Modbus mapping it looks like you can set up the MicroLogix as a slave over one of its serial ports. I found this on the web. Joe T. PLC+Modbus+Config.pdf
Sávio Pereira Posted June 18, 2019 Author Report Posted June 18, 2019 19 hours ago, Joe Tauser said: If you have a good understanding of Modbus mapping it looks like you can set up the MicroLogix as a slave over one of its serial ports. I found this on the web. Joe T. PLC+Modbus+Config.pdf 3.63 MB · 7 downloads Great! I´ll try it and let you know if it works. Thanks a lot!