AjaS Posted July 4, 2019 Report Share Posted July 4, 2019 Hi all, I use USC-P-B10 with USP-070-B08 (modular HMI/PLC) as a master via Modbus Ethernet. Could anyone recommend me how to catch an exception in UniLogic 1.26.90 if slave is not responsive (powered down, loose cable...). Thanks Link to comment Share on other sites More sharing options...
dierkens Posted July 4, 2019 Report Share Posted July 4, 2019 Take a look at the ping command. https://unitronicsplc.com/Download/SoftwareHelp/VisiLogic_Knowledgebase/Ladder/Functions/Communications-Ladder_Functions/Ethernet/Ping.htm Link to comment Share on other sites More sharing options...
AjaS Posted July 4, 2019 Author Report Share Posted July 4, 2019 14 minutes ago, dierkens said: Take a look at the ping command. https://unitronicsplc.com/Download/SoftwareHelp/VisiLogic_Knowledgebase/Ladder/Functions/Communications-Ladder_Functions/Ethernet/Ping.htm Thank you :))) Link to comment Share on other sites More sharing options...