In general, you have -5.0 to 56.0 mV range for the analog input. This means 610 values. You can make DT with 2 columns - one for analog reading (mV) and the second - for relevant temperature. each row in this table will have 2 MI = 4 bytes. The table wil lhave about 2.5 kBytes.

More precise, but much more complicated way is to read Raw value. In this case the resolution will be much higher, but making compare table - more complicated.