Power supply M91


Recommended Posts

  • MVP 2023

Hi,

As decleared in

https://unitronicsplc.com/wp-content/uploads/2015/12/IO-RO8_L-5408-0051-9.pdf

I0-R08 has 12VDC option -----  I0-R08L.

The main issue with expansion =  P-ON condition.

Both - PLC controller and EX-A1+IO-R08   IO must be powered from the same power supply.

By the way if you power M91-2-R1 and  EX-A1+I0-R08L from 12V

1. Both the OPLC and the EX-A1 must be connected to the same power supply.  
The EX-A1 and the OPLC must be turned on and off simultaneously.
2. The 12VDC power supply is supported by versions V2.00 (EX-A1) and later.
 
 

As for me you can power  M91-2-R1 PLC with power supply 12VDC and only galvanic isolated version EX-A2X+IO-R08 from separate 24VDC 

but  you must turn ON both PLC and IO at the same time.