Modbus Periodic Read and Write


job517

Recommended Posts

Good morning to all

I am using a USC-X5-TR22 PLC on unilogic version 1.32.98 (attached image shows core of the issue)

my question is how does the modbus read/write  is executed? Does it read the registers every 200 millisecond? Does it read sequentially or concurrently?

If so, is it safe for me to have so many registers that I am reading?

Also from the attached image you can see that I have a number of modbus devices from which I am reading the same amount of registers.

This system is currently running, all I want to know is if it will stay that way.

Thank you for your responses

Unitronics modbus register.png

Link to comment
Share on other sites

  • MVP 2023

If everything works and reading speed satisfies you - leave everything as it is.

To reduce the number of consecutive read / write commands, you should try to read not each address separately, but a lot of sequentially placed data by one command. In your screen you can see consecutive registers from one device 9-11, 20-28, 14-16. If you look closely at each device, it is possible to read all the data from it with one command and only in the PLC to extract the necessary data from the received packet. This recommendation has been successfully applied in this topic

 

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...