Gargamel Posted July 14, 2022 Report Share Posted July 14, 2022 Hi. After i added/enabled OPC UA in the plc and added one tag. Each time i make a change in the plc, i always have to reset it while downloading one small plc code change. In this example, i added a new local variable called "AAAAA" and added this rung and this small code. Before small changes like this, i could just download without reset the plc. Quote Link to comment Share on other sites More sharing options...
NoamM Posted July 20, 2022 Report Share Posted July 20, 2022 Hi Gargamel, checking your claim. Quote Link to comment Share on other sites More sharing options...
Gargamel Posted July 20, 2022 Author Report Share Posted July 20, 2022 When i removed all OPC UA configuration, reset became optional again. Quote Link to comment Share on other sites More sharing options...
NoamM Posted July 26, 2022 Report Share Posted July 26, 2022 Gargamel, Issue solved from UL 1.32.146 (firmware 1.32.157) - Please open a ticket on Unitronics "Help center" at https://support.unitronics.com/index.php to get this release. Quote Link to comment Share on other sites More sharing options...