Hello, New to using PLCs.

PLC: V700, V200-18-E3/4xb

 

https://www.amazon.com/dp/B0748BHLQL?ref_=cm_sw_r_cp_ud_dp_MPKEBK3VM6AV7174NC1Q

Pressure Transducer: 0-100psi

Output: 0.5V~4.5V linear voltage output. 0 psi outputs 0.5V, 50 psi outputs 2.5V, 100 psi outputs 4.5V.

 

I wanted to know how  would I setup the pressure transducer in the Hardware configuration....Analog Inputs...type...mode, as well as what settings to use for the linearization block.

 

Link to comment
Share on other sites

Hi;

Math required  for scaling.

In Hardware config, choose an analog Input on the  V200-18-E4/4XB

       0-10V  Input       ( there is no   0-5 V )

      Select an   MI to Store the raw value.

 

      In the ladder      us the Linearize function     Scale the Analog Output based on   0-10 V Input

                X Axis       0 to      16384    (   14 Bit Analog Input   -- 0 -1 0  V )                

                Y Axis       0  to   222         ( 0-100  PSI    100/45  x 100   )   If you want  0.1  PSI Resolution    2220

      Test from there

              

   DanT

Link to comment