DonM Posted September 13, 2011 Report Posted September 13, 2011 Hello, I would just like to check if there are any problems configuring a V570 to communicate on 2 separate Modbus RTU networks using PLC com ports 1 & 2 both using RS485? On one network the PLC would be a master and on the other a slave. Thanks. Best regards, Don.
MVP 2014 Simon Posted September 13, 2011 MVP 2014 Report Posted September 13, 2011 Hi Don, See the examples: C:\Program Files\Unitronics\Unitronics VisiLogic_C\Examples\Version 900\Project examples\Communications\MODBUS then look for V280_Modbus_port_to_port_test.vlp change the hwardware properties to V570 and download it. It sets one port as master and one also slave so you can do a loopback. Very handy when testing Modbus comms, so you can at least confirm if the PLC Modbus is working. Then you can plus in external masters/slaves.