I have looked for some basic information about pulse counting but I couldn't answer what i believe is a simple question?

I have some experience using the Vision series PLC for simple digital I/O and analog I/O. But I have a requirement to count pulse from a flow meter and plan to set up one of the inputs on the snap on module V200-18-E1B as a HSC linked to ML-95. 

I can make the connection to PLC direct or make a link between the flow meter device and the inputs to count the pulse with a PR Electronics 9202 pulse isolator. Then my scaled flow pulse should just increment ML-95. I am attaching some info on the flow meter compute pulse (max frequency 6.5hz. 

Just want to check I am understanding the function of the HSC input correctly.

Thanks

Paul

Flow meter pulse output specs.png

  • MVP 2023
Posted

You can connect the flowmeter directly to the -E1B high speed input.  Since the outputs on your flowmeter are "Current Sinking" (translation - NPN), you'll need a pull-up resistor connected to 24V power to make them work.  I recommend a 2.2K resistor.

image.png.dd840f65199639c01bb869393ab022d0.png

 

Joe T.