pedrofilipe Posted January 10 Report Share Posted January 10 Good, Variable ML9 in unitronics is equivalent to what Modbus address ? How do I see the ML9 address of the unitronics automaton in modscan32?s ? Quote Link to comment Share on other sites More sharing options...
MVP 2023 kratmel Posted January 10 MVP 2023 Report Share Posted January 10 You can find modbus address table in Visilogic Help Quote Link to comment Share on other sites More sharing options...
pedrofilipe Posted January 10 Author Report Share Posted January 10 Because , but what modbus address is the ML9? Quote Link to comment Share on other sites More sharing options...
MVP 2023 kratmel Posted January 10 MVP 2023 Report Share Posted January 10 ML0 ----7000hex ML9-----7009hex But you must know about different address table for Standard or Enhanced Vision PLC. Please post your PLC model Quote Link to comment Share on other sites More sharing options...
pedrofilipe Posted January 10 Author Report Share Posted January 10 thanks , PLC - V280 Unitronics ML9 TO what modbus address corresponds to the modscan32 ? the modbus address starts at address 40001 ? Quote Link to comment Share on other sites More sharing options...
MVP 2023 kratmel Posted January 10 MVP 2023 Report Share Posted January 10 V280 - standard Vision. This table must be used Then ML9 ----5109 in decimal format Quote Link to comment Share on other sites More sharing options...