Posts posted by AlexUT

  1. Hi Gonzalo,

    Do you use Gmail account?

    After all tests found that there is a Gmail problem.

    You have to check Gmail settings, or contact Gmail/Google to solve this.

    It is recommended to search Internet to find how many other Gmail users faced the same problem.

    B.R.

     

  2. 1. You cannot power these motors by Ladder PWM SCAN FB. It is very slow for DC motors.

    2. Right (MARCO) motor picture show remark "Do not use with PWM",  so you should use voltage regulator for this motor.

    And this voltage regulator should be managed by 4-20 mA, 0-10V, or PWM signal.

    3. Left picture motor may require the same regulators.

    *Both motors are 12V. Do you power PLC by 12 V?

    May be other Forum members has experience with such equipment?

    B.R.

     

    • Like 1
  3. " I currently have the PC and PLC set to address 192.168.1.4" confuse me.

    What is PC configuration?

    Do you use any router with DHCP settings?

    How it configured?

    Or you use LAN Switch?

    *You cannot assign the same IP address to 2 devices at the same LAN. It will not work.

     

  4. Would you like to use UniStream, which supporting SQL interface?

    UniStream supporting FTP file transfer as well.

    If UniStream is not an option - visit at next link:

    https://unitronicsplc.com/software-visilogic-for-programmable-controllers/

    and scroll down for "Programming tools for developers.

    Probably you can find one you can use.

    You can develop PC program which transfer required data between company server and PLC.

    B.R.

     

    • Like 1
  5. After reviewing your projects found, that you use normal closed SB 7 to activate all UniCAN Send at all projects.

    All scans at first 50 of 100 msec all RC1s and PLC are sending UniCAN packets.

    The only stopper is SB 202.

    So you flooding communication line by useless packets.

    It is recommended to replace SB 7 by SB 15, which is active for 1 scan each 100 msec.

    Hope this solve all your problems.

    B.R.

     

    • Like 1
  6. Hi,

    In common, SAMBA  and other PLCs are not intended to process images.

    But you have to provide more information to give you recommendations.

    -How camera is connected?

    -Does camera transmit picture, and what is a picture size?

    *SAMBA PLC is limited by memory size.

    -What information you should extract?

    Having more information from you about required operation forum members may recommend you next steps, or recommend better model, or recommend to forgot this...

    B.R.

     

×
×