Tejasvini Posted February 19 Report Share Posted February 19 Greetings!! I am new to visilogic and I have noticed two types of integer (system and memory) used in the plc programming software. Can anyone clarify the differences between these two types. Looking forward to hear from you. Tejasvini Yadav Link to comment Share on other sites More sharing options...
DanT Posted February 19 Report Share Posted February 19 Hi Tejasvini; The differences between SI and MI SI - System integers -- used by the PLC Operating system to provide feedback on system process Also Date and time are here. Gives status of Communications ( Modbus and Ethernet and so much more ) Basically most are read only for programmer to monitor and use in the ladder ( Date and Time can be edited) Anything starting with S SI, SB, SL,SDW are system variables. MI -- These are for you, the programmer to use in your progam as needed. Aslo MB, ML, DW -- These are backed up by the Battery, so on power loss, data is retained ( There is an SB for Battery Status ) XB,XI,XL etc are scratch pad variables for the programmer to use - you don't care if these get wiped on power fail. DanT 1 Link to comment Share on other sites More sharing options...
Cara Bereck Levy Posted February 20 Report Share Posted February 20 What Dan said 🙂 Check the following Help topics for more information: Link to comment Share on other sites More sharing options...