Dear all,

At this moment I'm working at communication by Ethernet with a scale. The scale needs and STX before and an ETX behind every message. When I fill manually the MI string range, it works.
For status request I have to sent STX 0 ETX, in the MI range this is in hex 02 30 03. I sent this with TCP_raw, so far everyting works.

I tried to use the function create excel delimeted line, but in here there is no option to use no delimeter (delimeter 1 cannot be empty).

If I use the funtion string to asci a cannot type the non printable characters like STX and ETZ into the string.

I look also at config protocol, maybe I could use it to fill a string but this is assigned to a com port.

Is there an easy way to fill a string with the STX before and ETX behind?

A MI is 16 bits ( 2 bytes) contains 2 characters. Is there a way to fill only the MSB or LSB?

Thank you in advance,

Gerard

Link to comment
Share on other sites

Dear Joe,

Thank you for your response attached the test program. To get status information from the weighing device I have to sent STX 0 ETX.

So first I convert 0 to ASCI. Then I insert STX before it, and then ETX behind it. This I sent with TCP raw send.

If I do a scan with TCP raw scan, I got the requested data. The data is 12 characters. What I see sometime is that there are 24 characters available (2 times the status information) behind each other. I thought maybe it's better do a raw scan after a short period when I did the raw send, but that doesn't matter. If I monitor ethernet in setup mode, I see it also. Sometimes I got 2 status strings f the weighing device.

Socket 0 I configured for remote assistance or programming purposes. Socket 1 I configured to communicate with the weighing device.

All help/information appreciated!

regards,

Gerard

 

V1210 com test1.vlp

Link to comment
Share on other sites

Update, I changed the port number of the scale to 32049, because I cannot give in a higher port number in the TCP config protocol. Then I start using the TCP config protocol and this works convenient to build the string to sent.
Attached the test program. Anyway It seems that we miss one scan cycle. If you see the picture attached you see that the number of TX is not the same as the number of RX. In this case if I do one manual scan (M91) they become equal, I 'm able to read data again and then they are equal. I thought it needed a delay between the sent and scan function, there for a changed to a negative edge to start the scan function. Anybody an idea?

Is it a problem to do a scan every cycle (keep scanning)?

20241023_142838.jpg

V1210 com test2.vlp

Link to comment
Share on other sites

  • MVP 2023

When you say "cycle" I'm guessing you mean every PLC scan.

Yes, that's a problem.  You can't do it without clogging up the buffer on the PLC.  The TCP protocol is by definition a handshaking protocol - when you send a request you have to wait for an answer, which probably explains why you have more transmits than receives in your picture.

I took a quick look at your code.   The protocol blocks are a higher level of complexity and it's easy to not implement the properly.

1.  The SCAN block is the listener and should be on the rail.  You're always listening.

2.  In the SCAN block, you only have one message (message 0) and the way you have it configured it will register if and only if it starts with hex 02 and ends with hex 03.  Put a second message in that is a string only and have it point to a different MI area.  Make its length twice as long as you anticipate so you don't miss any incoming messages.

3.  You need to verify that the socket is connected with a system bit before you call the SEND block.    

 

Try these out and let us know what you find.

Joe T.

Link to comment
Share on other sites

Hi there,

Attached the final version which is working fine.

I put the TCP scan on the rail.

I tried with and without Joe’s suggestion to add a second message to scan, but it worked perfect in both methods, so didn’t use the second message.

I see no missing scan results anymore (amount TX = amount RX). I added also some conditions that the NIC should be initialized before you can connect. And it should be connected before you can do a protocol configuration.

I did some tests with removed ethernet cable and powered off scale, to see if it reconnects automatically and everything seems to be ok.
There is no option to give in a higher port number as 32767 in the Protocol TCP/IP configuration?

V1210 com test3.vlp

Link to comment
Share on other sites

Hi, yesterday I had problem with printing visilogic, it crashed every time. I used v 9.8.96. In a hush I decided to update Visilogic, hoping the printing problem was solved. I updated to the most recent version 9.9.1. After this I got messages to add info password and PCOM password in program. It took me a while to find out how I had to solve this, but I managed. When downloading the program I had to update OS etc. At the end everything seems to work again. Except I monitorSB148 (Ethernet: Socket 1 Connected), is that this goes down every 5 seconds and immediately goes up again (because in the program it will reconnect). I did not see this before. Anybody has a clue?

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...

Important Information

This site uses cookies. By clicking I accept, you agree to their use.