Need a solution for loop powered Fisher valve


Recommended Posts

I have a customer that has "sprung" the installation of a pneumatic actuated Fisher V6100 series valve. The valve is a modulating valve to be run from a 4-20ma signal. Here is my problem the valve requires 10Vdc minimum to be able to actuate at all. The Unitronics is not a loop power capable device and does not send out 10VDC untill about 18ma (or so).

I am using a V570 with an IO-Ai4-AO2 remote module to try and actuate this (I also have a V200-18-E6B module). Since the PLC is not able to provide what the valve needs. I need a best suggestion on what hardware anyone has used to isolate/amplify an output 4-20ma signal that is capable of providing the r4equired loop power.

Any help is welcome

Thanks all

Keith

Link to comment
Share on other sites

I have the same problem with Spirax Sarco pneumatic positioners. I use the Seneca K109UI to overcome this problem but most isolating transmitters should cope.

http://www.senecauk.com/acatalog/K109UI.html

The K121 might also work for 4-20mA and is cheaper for me.

http://www.senecauk.com/acatalog/K121__Universal_Isolated_Transmitter_with_2_Wire_-_Loop_Powered.html

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...