Bazel27 Posted June 6, 2014 Report Share Posted June 6, 2014 Hello , Need some help. I have NTC sensor 10k Ohm at 25 C , connected through the voltage divider to Jazz 10-11-ua24 analog 0-10V input. When divider is not connected to plc , and i measure voltage between R1 and ground it shows 5 V , and then i connect it to the plc , voltage drops to 4V. What is the reason ? i have made a drawing of connection diagram Thanks in advance Bagel NTC calibration.spl7.pdfAleksei Quote Link to comment Share on other sites More sharing options...
MVP 2021 Joe Tauser Posted June 7, 2014 MVP 2021 Report Share Posted June 7, 2014 You're adding a resistor in parallel to R1 when you connect the analog input; the spec lists 20K ohms as the input impedance. The effective resistance (Re) below the sensor will be 6.67K. Applying the voltage divider formula Vr = Vs*Re/ (Re + Rs) = 10 * (6.67) / (6.67 + 10) = 4.00 You're going to have to re-size R1 to compensate for the input impedance of the module. I'll leave that as an exercise for you. Or you could just adjust your scaling logic. Joe T. Quote Link to comment Share on other sites More sharing options...
Bazel27 Posted June 9, 2014 Author Report Share Posted June 9, 2014 You're adding a resistor in parallel to R1 when you connect the analog input; the spec lists 20K ohms as the input impedance. The effective resistance (Re) below the sensor will be 6.67K. Applying the voltage divider formula Vr = Vs*Re/ (Re + Rs) = 10 * (6.67) / (6.67 + 10) = 4.00 You're going to have to re-size R1 to compensate for the input impedance of the module. I'll leave that as an exercise for you. Or you could just adjust your scaling logic. Joe T. Thanks , i have made an adjust of scalling logic already. Thanks for the fast response. Cheers Aleksei Bagel Quote Link to comment Share on other sites More sharing options...