I have NTC sensor 10k Ohm at 25 C , connected through the voltage divider to Jazz 10-11-ua24 analog 0-10V input.  When divider is not connected to plc , and i measure voltage between R1 and ground it shows 5 V , and then i connect it to the plc , voltage drops to 4V. 

What is the reason ?

i have made a drawing of connection diagram

Thanks in advance 

 

Bagel NTC calibration.spl7.pdfAleksei 

  • MVP 2023
Posted

You're adding a resistor in parallel to R1 when you connect the analog input; the spec lists 20K ohms as the input impedance.  The effective resistance (Re) below the sensor will be 6.67K.  

 

Applying the voltage divider formula Vr = Vs*Re/ (Re + Rs) = 10 * (6.67) / (6.67 + 10) = 4.00 

 

 

You're going to have to re-size R1 to compensate for the input impedance of the module.  I'll leave that as an exercise for you.  Or you could just adjust your scaling logic.

 

Joe T.

Posted

You're adding a resistor in parallel to R1 when you connect the analog input; the spec lists 20K ohms as the input impedance.  The effective resistance (Re) below the sensor will be 6.67K.  

 

Applying the voltage divider formula Vr = Vs*Re/ (Re + Rs) = 10 * (6.67) / (6.67 + 10) = 4.00 

 

 

You're going to have to re-size R1 to compensate for the input impedance of the module.  I'll leave that as an exercise for you.  Or you could just adjust your scaling logic.

 

Joe T.

Thanks , i have made an adjust of scalling logic already.

Thanks for the fast response.

Cheers 

Aleksei Bagel 

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...

Important Information

This site uses cookies. By clicking I accept, you agree to their use.