protechnologia Posted June 9, 2014 Report Posted June 9, 2014 I have a signle PLC over Ethernet configured in UniOPC. Why if I set Update Rate to value higher than 3 sec, (00:00:03:00) after couple of seconds values in UniOPC freezes and stop changing?
protechnologia Posted June 11, 2014 Author Report Posted June 11, 2014 I probably found my answer. It was due to SI103-106 operands. I had them set to 50 causing to disconnect after 5 secs.