Theoretically, there is no problem to use it as stand alone PLC. But please note - there is no battery inside, so on power off it will loose all operand values. If this is not a problem...

When turned off, would the RC1 also loose the ladder program, i.e., does the application program need to get re-downloaded?

Link to comment
Share on other sites

  • External Moderators

Blitz - The Application Program is never lost when the Unit is Powered Down, but any Operand Values are lost.

OSUstamm - Might I recommend some sort of 24vDC Battery Backed Power Supply? I've used a few in New Zealand that will basically run off Mains power all the time until the Mains is lost and then switch to the Batteries which on an EX-RC1 with a 12Ah 24v Battery you could expect over 12 hours of backup :)

Link to comment
Share on other sites

Blitz - The Application Program is never lost when the Unit is Powered Down, but any Operand Values are lost.

OSUstamm - Might I recommend some sort of 24vDC Battery Backed Power Supply? I've used a few in New Zealand that will basically run off Mains power all the time until the Mains is lost and then switch to the Batteries which on an EX-RC1 with a 12Ah 24v Battery you could expect over 12 hours of backup :)

Hi Ash,

Thanks for the reply.

Some more questions. Would it be possible for expansion I/O's via EX-RC1 and two Vision Controllers (e.g., V570's) all linked in CAN to implement the following:

1. EX-RC1 I/O states and operand values transmitted to two V570's? For example, 60 temperature values or 100 pump states simultaneously updated to the 2 V570's.

2. Either or both V570's sending write commands to the same EX-RC1 linked output channels and/or operands? For example, can either or both V570 send an on/off command to a relay output and/or write a numeric value to the same analog output channel?

Link to comment
Share on other sites

  • External Moderators

Blitz,

Yes to the first and Yes to the second :)

1) In this case you would need to use the UniCAN Functionality. The EX-RC1 can send messages constantly to both Vision 570's. Remember with 16 MI's per UniCAN Send Function, you can send up to 512 Registers 16 MI's x 32 Messages in a single Program Scan.

2) Both Vision 570's can send UniCAN Messages to the EX-RC1 to control MI's for Analog Outputs and Output Operands for the Digital Outputs. If both Vision 570's were to change an Analog or Digital Output, the last Vision 570 to send a UniCAN Message would set the final Operand Values.

UniCAN is a very power tool within Unitronics PLC's. Combined with the EX-RC1 it's excellent!

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...

Important Information

This site uses cookies. By clicking I accept, you agree to their use.