Yes, this is a current product. There are not any tips as you only need to upload the file to the gateway after creating it with the configurator. There are instructions in the manual which you find linked below:

 

http://www.unitronics.com/docs/technical-library/gw-bac1.pdf?sfvrsn=0

 

A Unitronics PLC will be set up as a Modbus master over RS485 or Ethernet and communicate to the gateway. The gateway has it's own registers and will convert the Modbus registers to BACnet registers. This then allows any BACnet device to also connect over RS485 or Ethernet to read/write information to the gateway.