Jump to content

Programing analog I/O


Recommended Posts

Hello

I just bought a Unitronics M91-2-UA2 PLC.

I am trying to program the analog I/O, but I cant get them to talk together.

I have a loop calibrator on the analog input 4-20ma.

On the analog output i have a multimeter that i can recieve 4-20ma. 

The problem is when i give the input 4ma, the output showa 16ma. When I adjust the input to 8ma, the output shows 12ma... 

Can anyone help me with the ladder diagram to get the output to communicate with the input.

 

Link to comment
Share on other sites

  • MVP 2023

It's been so long since I've played with an M91 I may have forgotten some of their idiosyncrasies.  It sounds like the scaling is still off.

Have you played with different constant values?  You're not going to break the PLC by trying. 

I think I know what value you need to stuff into SI 82 but I wouldn't want to take your fun away.  Beat on it and let us know what you find.

Joe T.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...

Important Information

This site uses cookies. By clicking I accept, you agree to their use.