6 hours ago, Gabriel Franco said:

Use LINEARIZATION FB.  Keep in mind module resolution is 0.1°C, that´s the reason X1 and X2 values are -2000 ... 6000 in the image

 

image.thumb.png.47a364468b5f8e809173b98040403f6b.png

I’m using it. X1 i putted -2000 and x2 is 6000.y1 is 0 and y2 is 4095 because i/o module is 12 bits. Is it possible to put -200 and 600 because bodule can take od from -50 to 460?

Link to comment
Share on other sites

1 hour ago, Isakovic said:

You don't need linearization for PT100. Module itself does that and gives you result x10 (value 123 would be 12.3 degrees). You just choose °C or °F in hardware configuration.

I tried that too now, and i got diferrence 2 *C ( other mesuarment is with Ic camera and with fluke 289 multimeter)

Link to comment
Share on other sites

Pt100 are resistive probes, error could be in cable resistance (if cross section of those 3 wires is not the same), in some bad contact or EM interference. If those 2 °C is static error you could add offset in the program to take it into account or try filtering it.

Link to comment
Share on other sites

  • MVP 2023

An IR camera is no where near as accurate as an RTD probe due to variances in emissivity of the surface being looked at and the setting in the IR sensor.  In fact, an RTD or thermocouple is to calibrate all IR devices.

I'm not sure how you're using the Fluke 289, as it does not have 4-wire lead compensating resistance.

I would believe what the RTD module is telling you over the other two instruments.

Joe T.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...

Important Information

This site uses cookies. By clicking I accept, you agree to their use.