Jungletron Posted November 3, 2020 Report Share Posted November 3, 2020 Hi, I was hoping to use URA-0800O (AI08O) or URA-0400O (AI04O) to get the 4-20 mA signals from Hanna transmitter (EC and pH). From the Hanna transmitter manual HI 98143-20 is 4-20 mA passive and HI 98143-22 is 4-20 mA active and in the last page: Questions: 1 - Is the HI 98143-22 compatible with Unitronics sink type analog inputs ? (and the HI 98143-20 not compatible ? ) 2 - Is the 2 Input Common(AGND) to 4 Input Common(AGND) difference between the URA-0800O (AI08O) and URA-0400O (AI04O) relevant for this choice? Already found info in the forum about double sinking and I really do not want to mess this ... Thanks for any help in advance! JT Quote Link to comment Share on other sites More sharing options...
MVP 2022 Joe Tauser Posted November 4, 2020 MVP 2022 Report Share Posted November 4, 2020 I'm guessing you've already seen this post- The -22 should work. The -20 won't. Joe T. Quote Link to comment Share on other sites More sharing options...
Jungletron Posted November 4, 2020 Author Report Share Posted November 4, 2020 I have seen that post and this and this but was still not sure. Thank you very much! JT Quote Link to comment Share on other sites More sharing options...
Isakovic Posted November 5, 2020 Report Share Posted November 5, 2020 I'll jump into this discussion because I am little confused here. More so after reading other quoted forum posts. Why wouldn't HI 98143-20 work? From the technical description I would wire it like this: Like any other two-wire 4-20mA transmitter. Is something not right here? Quote Link to comment Share on other sites More sharing options...
MVP 2022 Joe Tauser Posted November 6, 2020 MVP 2022 Report Share Posted November 6, 2020 @Isakovic- Because the -20 is not a two-wire transmitter. It's a powered device with two outputs - pH and conductivity. You have to zoom into the above diagram to see the rest of the story: The power supply negative is connected to the loop negatives. This is a sinking loop output and absolutely ridiculous. In your diagram, take the negative of your 24V power supply and connect it to the 0 on the HI 98143-20. You'll immediately see the problem. If we had isolated analog inputs this could be made to work. But, alas, we do not. Joe T. 1 Quote Link to comment Share on other sites More sharing options...
Isakovic Posted November 7, 2020 Report Share Posted November 7, 2020 Oh I see it now! If the PLC and Hama are powered from the same supply both CH1 and GND on the PLC module will effectively be on the ground potential. Now I suspect AI08O also has GND and negative power terminal connected, so switching terminal places would not work. But will it work if separate power supply is used only to power Hama (not referenced to the ground), and other supply is used for current loop and PLC? Quote Link to comment Share on other sites More sharing options...
BabbRust Posted June 18, 2021 Report Share Posted June 18, 2021 Hi...In the event that the simple data sources are secluded, simply wire in arrangement.On the off chance that they are not secluded, wire to one as 4-20 mA, wire to the next as Voltage in equal.Wire to one PLC as a 4-20 mA contribution, from that PLC wire a simple Output to a contribution on the other.Before PLCs became basic collectors were wired in arrangement constantlyTransmitter, Controller, Chart-recorder, Alarm unit and so forth Wiring in arrangement you simply must be cautious you don't run out of force supply Voltage, study the transmitter manual. Quote Link to comment Share on other sites More sharing options...