4-20 mA signal from Hanna transmitter


Jungletron

Recommended Posts

Hi,

I was hoping to use URA-0800O (AI08O)  or URA-0400O (AI04O) to get  the 4-20 mA signals from Hanna transmitter (EC and pH).

From the Hanna transmitter manual

HI 98143-20  is 4-20 mA passive

and HI 98143-22 is 4-20 mA active

and in the last page:

image.thumb.png.d51f0199948df9ad022a748bc4f17071.png

Questions:

1 - Is the HI 98143-22 compatible with Unitronics sink type analog inputs ? (and the HI 98143-20 not compatible ? )

2 - Is the 2 Input Common(AGND) to 4 Input Common(AGND) difference between the URA-0800O (AI08O) and URA-0400O (AI04O) relevant for this choice?

Already found info in the forum about double sinking and I really do not want to mess this ...

Thanks for any help in advance!

JT

Link to comment
Share on other sites

I'll jump into this discussion because I am little confused here. More so after reading other quoted forum posts. Why wouldn't HI 98143-20 work? From the technical description I would wire it like this:

Capture.PNG.9cc5ebb1f776fc1ed4556954d2a71fd5.PNG

Like any other two-wire 4-20mA transmitter. Is something not right here?

Link to comment
Share on other sites

  • MVP 2023

@Isakovic-  Because the -20 is not a two-wire transmitter.  It's a powered device with two outputs - pH and conductivity.  You have to zoom into the above diagram to see the rest of the story:

image.png.2653d2e06a0b2b5f6ae366b0e2c75e26.png

 

The power supply negative is connected to the loop negatives.  This is a sinking loop output and absolutely ridiculous.  In your diagram, take the negative of your 24V power supply and connect it to the 0 on the HI 98143-20.  You'll immediately see the problem.

If we had isolated analog inputs this could be made to work.  But, alas, we do not.

 

Joe T.

 

  • Like 1
Link to comment
Share on other sites

Oh I see it now!

If the PLC and Hama are powered from the same supply both CH1 and GND on the PLC module will effectively be on the ground potential.

Now I suspect AI08O also has GND and negative power terminal connected, so switching terminal places would not work. But will it work if separate power supply is used only to power Hama (not referenced to the ground), and other supply is used for current loop and PLC?

Link to comment
Share on other sites

  • 7 months later...

Hi...In the event that the simple data sources are secluded, simply wire in arrangement.On the off chance that they are not secluded, wire to one as 4-20 mA, wire to the next as Voltage in equal.Wire to one PLC as a 4-20 mA contribution, from that PLC wire a simple Output to a contribution on the other.Before PLCs became basic collectors were wired in arrangement constantlyTransmitter, Controller, Chart-recorder, Alarm unit and so forth

Wiring in arrangement you simply must be cautious you don't run out of force supply Voltage, study the transmitter manual.

 

 

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...

Important Information

This site uses cookies. By clicking I accept, you agree to their use.