JRstabile Posted August 29 Report Share Posted August 29 I have been trying to use a RC15 as a motor step intermediate between a V700 and a Sputtering system stepper motor. it was going well until I tried to upload a test program to the RC15, Apparently PTO functions are not supported and start up bits are invalid. Any one have some advice I'm at a loss. Quote Link to comment Share on other sites More sharing options...
Gabriel Franco Posted August 29 Report Share Posted August 29 Rung 1: change from SB2 transition contact to normal contact. Make sure the PTO config has appropiate channel definitions. Quote Link to comment Share on other sites More sharing options...
MVP 2022 kratmel Posted August 29 MVP 2022 Report Share Posted August 29 Please find PTO example for EXF-RC15 module in Visilogic Hepl menu. Quote Link to comment Share on other sites More sharing options...