  1. 14 hours ago, Jeff164 said:
    • 24 volt power to pin 1 of transmitter from instrument power supply.
    • 0 vdc to pin 2 of transmitter and pin 2 (0V) of Samba input terminals 
    • 4-20 mA signal from pin 3 of transmitter to pin 10 / I5 of Samba

    And JP4, JP10 set to B - enough to get the right analog signal in "Source" transmitter mode. Please Note I5 >>>>> AN3 analog input. 

     

    14 hours ago, Jeff164 said:

    All Samba jumpers will be set to B except 11. 

    I think you want to setup 3 channel temperature mesurement via Samba. In your configuration present Two PT100 sensor and you need to use transmitter for set channel #3 PT 100 to 4..20mA and connect it to AN3 analog input.

    If it is true - you must set J11 to B also.  

    Then you can connect both #1 and #2 PT100 sensor Common wire to CM PT100 (I11 Samba pin). 

  2. Hi,

    maybe you do not know - Unitronics do not offer embedded simulator in Visilogic and Unilogic.

    If you have Unistream on table - you can go online and test your code. You do not pay for software but must test program downloaded to  PLC.

    If this function do not work in program downloaded to Unistream PLC - you have another rung in program with the same coil -(  )- Name or this subrouting is not called from main program.

    Only one direct coil must be used in program.

     

    In TIA you can use simulation and  run ladder without PLC. But you must pay for software licence and PLC separately.

     

  3. Try to use Ethernet cable. You can touch on right-up corner of USP screen for some time and find Uni Apps menu. In this menu you can find Ethernet connection IP.

    Use it for Unilogic communication setup. 

     

    About USB... If you try to install Unilogic without Run as Admin option  - some part of drivers can be blocked. 

    On my PC if i connect USP via USB - Unilogic agent say about connected USP in down-right corner of PC screen.

     

  4. Hi,

    Please print printer configuration. You can read in manual how to press button on power on.

    Please post foto of this configuration. As i see maybe something wrong in printer input source. I sometimes have problem with not operational port on  Zebra (USB, COM or Ethernet). It is appear after automatic flash optimisation that printer do sometimes (if user sw off printer when it is performed - printer firmware corrupted).    Manual switch print source help to solve problem (if it wrong on paper).

     

  5. Please use demo project from Visilogic

    V120_Store_Load_Timer_or_Counter.vlp  from Function example.

    For store timer time left  SB2 -|/|-   system bit can be used.

    After power on SB2 -| |- can restore timer value.

     

    V120_Backing_up_a_HSC.vlp  demo Project in Visilogic  is helpful for understand how to store-restore operation work.

     

  6. 2 hours ago, mydlochu said:

    deletes all received SMS, not just the 'read' ones.

    I do not know how you send test SMS to PLC.

    In one of my project i use incremented number after "status" message.

    Something like password001 - PLC send back password002..... I send this password002 to PLC - answer: password003 ect.

    In this way only different message is stored into modem And i only copy message from PLC for check status -no need to type new one. 

    Yes all message  is cleared after comm restart. But i always know last number and can send bigger one

  7. The UniStream® platform comprises CPU controllers, HMI panels, and local I/O modules that snap together to form an all-in-one Programmable Logic
    Controller (PLC).

    USP-070-B10 is HMI panel - it is no battery backup RTC inside. CPU for panel (PLC CPU) with embedded battery  must be connected to panel for provide RTC.

    Is it CPU connected to panel or you use only panel without PLC CPU?

  8. If it is possible to connect to old PLC - you can read operand and save it.

    After download project to new PLC - you can write saved operand from file.

    I think you simply do not remember  timer value setup  and if it resetted to 0 - blinking is normal behavior :)

×
×