Posts posted by kratmel

  1. In my Jazz application i use another idea to run time mesuring.

    I use MI for set time (in sec or 0.1sec)  and copy it to another decremented MI. Then SB with 1s or 0.1s  blink used for dencrement this MI.

    If decremented time MI  <= 0 - do something. At start of next cycle simple copy set MI to decremented MI.

    Then my STATE MACHINE worked with timed cycle and do not use timers.   

  2. Due to the fact that you have replaced the full version B10 of the controller with a simplified basic version B5, the functionality you have programmed probably does not meet the capabilities of a simpler PLC controller.

    That is, if you wrote a program from scratch for a simpler controller - probably the Unilogic environment would tell you that some of used functions are not supported.

    By making a simple replacement, you have avoided the messages of the Unilogic environment, but probably both used controllers are not equal in capabilities.

    Some option in Unistream built-in manual is marked with "For UniStream 7″ Pro only".

    • Upvote 1
  3. This is realy old SIKO IG 11 series abx-1000-3-pp

    It is also strange for me 1000x4=4000 increments. 

    But it is present on Jagenberg macnine cirquit diagram = 1000ppr.

    Jagenberg.thumb.jpg.7f6e9af23ab4e42e62f0af93e4de09b3.jpg

    Main goal - start-stop overtaking hooks on Startposition - 150 pulse after Z pulse (120degree) and 1_Stopposition - 1200-1300 pulse after Zpulse.

    Than if Z pulse losted - machine do not stop in Start position.

    Than 1 ppr error is not problem. Main problem -  do not lost every Z pulse.

  4. Thanks Joe, i have on shelf one of

    1 hour ago, Joe Tauser said:

    24V pulse stretcher

    I was already thinking about testing this device.

    However, in the process of analyzing the already assembled circuit, I came to the conclusion

    that I can rearrange the input signals and try to use the third counter, which is on board the applied PLC.

    Then now i have two possible solution and can test it on machine.

    I wonder if there are any other options?

  5. Hi,

    In my last application I use V130-33-TR20 PLC.

    Applying an interrupt  (1.25ms), I was able to get a system that controls the clutches to drive the mechanism.

    As always happens in the process of modernization of the old production machine - it had to work at low speeds provided by the manufacturer, but as a result, customers wanted to triple this speed.

    Accordingly, the applied control algorithm began to give unpredictable failures at increased speed.

    After analyzing the problem, I realized that the encoder used in the machine has three additional Z pulses per revolution.

    Z pulse has a length equal to one pulse of the encoder (1000ppr used).

    Accordingly, the interrupt method (Immediate read input) used to interrogate this
    Z pulse sometimes does not "see" a too narrow pulse at increased speed.

    My idea is to use another HSC (MI1) channel for find Z pulse (count it) in interrupt routine.

    Interrupt.JPG.965d43d90441ffc29e5336700dd4d0b7.JPG

    So my question is:

    What other tricks can be used to ensure the recording of a short  Z encoder pulse?

     

    P.S. The accuracy of the definition does not play a decisive role. (+-50  main encoder pulse possible).

    However, skipping the definition of this pulse leads to damage to one part produced by the machine. 

  6. Hi,

    maybe some next step help to find solution:

    1) Try to use separate USB to COM converter and PORT1 of  V570 to run connection (V570 com port CS cable needed). This is for Visilogic installation check. Result?

    2) Try to use short USB cable for V570 connection ( For test power +5V from Laptop to V570). Result?

    3) (the same test as #2) Try to use USB hub with external power for connect USB V570  to Laptop. 

    4) Try to change COM port # used by V570 USB-com driver in system and try to use com port # do not used by another drivers.

    5) Last steps on video from DELL (2021)

    https://www.youtube.com/watch?v=xRnferpaMBU

     

    P.S. Maybe it was only Win10  issue (update, antivirus, UAC, ect.)

    P.P.S.   Try to go to V570 info mode and check  is it any information sended  to V570 when Visilogic try to connect.  You can check it on working and not working Laptops. 

  7. Quastions;

    1 What expansion module used EX-A1X or EX-A2X?  EX-A2X is isolated and more stable.

    2 How much W is power supply capacity? If it low - install NEW another one with more A on 24VDC outputs

    3 Is it possible that on output present relay or valve coils without diode clamp?  If Yes - install diode clsmp to all coils

    4 Is it some VFD installed near PLC - if Yes - please connect -24V power supply wire to machine GROUND (EARTH).

    5 Is it possible that on some output present short circuit? And some times PLC  activate this output and restart PLC with error?

     

  8. 18 minutes ago, Ausman said:

    audiophile with the most expensive valve amps and super duper turntable sitting back with their $10K headphones on

    You are right, Aus!

    ....one of this audiophile (with self made and expensive valve amps and expensive headphones and speakers)  - my friend posted photo of this vinyl from collection on local forum. 

    Maybe now this vinyl record is already a very expensive antique!

×
×