Right, but you also must check current step to make sure you are moving to desired step. It´s also posible to jump to a step other than next one.
-
Then you have to set duration time equal 0 to those steps you want to move by external signal rarther than by time. In ladder, you must use your own conditions and current step index drum sequencer to move next (Or desired) step
-
Drum sequencer is used to set outputs only (Physical or MBs), so I don´t understand why you want to use inputs. Or do you mean using inputs to move between steps?
-
Have you checked operand values for frequency, duty cycle and MB that turns PWM on?
If those operands are all set to 0, PWM will not work at all. It can be the cause your second unit doesn´t work either.
-
Perhaps a number greater than 327.67 ??
Also check entry limits.
-
Take a look to:
C:\Program Files\Unitronics\Unitronics VisiLogic_C\Examples\Version 900\Project examples\Data Table\V280_Function_Block_Multi_Process_via_Data_Tables.vlp
-
Thanks for info, it´s ver useful.
I´ve always expected to be able to set default (My default) timer preset values such as any other operands, using power-up initialize option.
Those timers which user must not modify, I preset using ML and store timer preset function in ladder.
Clone should be complete.
-
Lukas, number of rows are fixed when you create/edit data table. There´s no way to modify it by ladder.
Usually I use a pointer to know which row I must write data from. In that way you know how many rows are available.
-
I´ve done same application but for security reasons using pneumatic switches and AND gate to close clamp and opening it with electrical signal. This way clamp only closes if operator pushes both switches at the same time (With slight time delay).
-
Only 4 active connections socket connections. That is correct.
But doesn´t mean only 4 slaves can communicate with a master, does it ?
Is it possible using a single socket communicate with multiple slaves ?
-
I suggest you to use a loadcell simulator to narrow the problem. Perhaps a loadcell drifted with a no-steady behaviour
-
Maybe using list of texts variable with keypad entry enabled, pointing to an MI, but you have to press up/down keys to change value
-
I´ve used this procedure to write a single MI register:
Public Function SetMIValue() As Integer
Dim MI() As Integer
Const Address As Integer = 12
ReDim MI(0)
MI(0) = 433
SetMIValue = mComDriver.Write_MemIntegers(Address, 1, MI)
End Function
-
You can also use Hardware Configuration, setting high speed input as HSC and frequency measurement linked to an MI or ML. It will give you Hz directly, however its resolution is just 1 Hz.
You must check your wiring as well.
-
You can use "load timer/counter preset" and "Store timer/counter preset" functions to do that.
-
In ID=4, why do you use #4 as destination in UniCAN Send, Arrived and check alive FB´s? As I understand, it should be #1 to proper communicate with master PLC
-
I had same issue a few months ago, using USB-serial converter I was using for years with no problem. And yes, problem was with converter. Just replaced and everything works fine to me since then.
-
Anyone knows a way to connect USB bar code scanner to RS232 serial port of V130 ?
I already tried using regular USB-Serial converter, but didn´t work
-
Only analog inputs #2 and #3 are current/voltage configurable, by jumpers and software.
#0 and #1 are for TC, RTD
-
Just open datatable and place mouse pointer over cell you want to get memory allocation. It shows type of register, length and allocation (FLASH: ## or RAM:##).
- 1
-
I haven´t noticeddifference between writing to registers or database.
Based on frequency you have to record data, I would use database also to getdata from PLC to PC.
-
Thanks Simon, I just wanted to be sure
-
Can EX-RC1 have IO-LC1 or IO-LC3 attached and to be programmed to act as a single and stand-alone bulk-weighing scale controller?
I have 8 scales site-distributed along factory which do not need local display, just local control; but to be monitored from control room. My idea is to have one main OPLC to monitor and distribuited control.
-
You may consider using drum sequencer for such application, even you have fixed times between states (Which makes it easier) or programmable times
IO-AI4-AO2 reading problem
in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Posted
Hello all.
I just moved an application from V130-33-TA24 to a V1210 using local I/O and remote via EX-RC1, including IO-AI4-AO2.
V130 used one analog input configured as 4-20 mA coming from a weigh scale indicator which has passive analog transmitter. It uses external 12 VDC power supply (Device requires 8-15 VDC as external power supply) different from the 24 VDC used for OPLC. It worked fine for months.
Now, using IO-AI4-AO2 for same purpose and wired the same way, analog input raw value doesn´t move beyond 10.
Tests already performed:
The only relevant difference I found between analog module and V130 is impedance for analog inputs.
It seems like this particular transmitter is not compatible with IO-AI4-AO2. I have no information about maximum impedance load from transmitter.
Using a resistor in parallel with analog input would be useful?
Any suggestion would be appreciated.