Posts posted by Gabriel Franco
-
-
I guess the better option is to encrypt sensitive data such as password. This can be accomplished using math calculation in ladder when reading and writing from/to database. User may be able to see datatable but encrypted password.
Other way, would be using registers to save such information.
-
Based on your latest post, what you need is a PID with PWM digital output. There are examples you can look at
- 1
-
Do not use positive transition of SB13, instead, use N.O. contact.
-
Already fix it updating OS to PLC.
-
Attached image showing wrong ASCII keypad.
Any idea to fix it.
- 1
-
Update OS, download a blank project, then download your project again.
-
Alexander, it was not my case, because I had to downgrade Visilogic version (From 9.8.18 down to 9.7.0) to be able to upload PLC project.
-
PLC: V290-19-B20 (A) O/S 5.04(23).
In info mode, under Version PLC shows DB 27, creation ver 4.0.06, modification ver 9.7.09
Visilogic 9.8.18 Build 0
I cannot upload PLC program to my laptop.
Attached reported error.
What does it mean and how can I upload program?
I´m going to download Visilogic V9.7.0 and try again.
EDIT:
I could upload PLC program using Visilogic V9.7.0 Build 0
-
I also noticed it earlier when using previous versions of Visilogic and it forced me to include the same workaround in my programming standard. To be honest, I hasn´t tested with latest version.
-
Can you ramp PID setpoint up at the desired rate? You might need to adjust PID parameters on the road to achieve a better control.
I don't know about kiln process, but used this approach once to control a motor speed.
-
Is the legacy snap V200-18-E3B fully compatible with recent V200-18-E3XB ? I mean, dimensions, connections, electrical specs ?
-
I use UDP instead TCP and doesn´t need so long delays between devices because no need to open/close socket, only a short delay between devices (50 ms or so).
- 1
-
Connect 0Vdc of PLC Power Supply with 0Vdc of external PS.
-
Is there a simpler way to set same duration time for all drum other than doing it step by step, like row and column SET/RESET option?
-
Try writing to 8500 instead of 8501. Just a wonder. I have not had addressing issues with Schneider VFDs but with power monitors.
-
I suggest you to read any reading parameter, to make sure comms are ok.
Did you properly set parameters to control VFD via MODBUS? (fr1, add, tbr, .... )
-
John,
RUN: Write 000F(hex) to address 8501, and desired freq. to 8502.
STOP: Write 400F(hex) to address 8501. Stop mode depends of your VFD configuration.
-
John, take a look to:
It´s for ATV31 but I´ve used for ATV312 as well.
-
PV low limit: -60
PV high limit: +60
CV low limit: 0
CV high limit: 10000 (Equivalent to 100.00% with 2 decimal places), then you must linearize CV to your analog output to 0 ... 5 V, using X1 = 0, X2 = 10000, X = CV. Y1 and Y2 values depend of your analog output card.
-
Hi Don, I´ve used MOXA NPort W2150A
-
The number of rows are fixed. You can use empty rows set with zeroes, so you can use "datatable find" tool to get last row with valid data.
-
Check on help files, searching battery back-up. There´s a topic explaining this behavior
-
OPLC: V570
Visilogic: 9.7.47
Hello all.
I want to show a small pop-up window for START/STOP buttons in such way I have a single place to control several motors. Such pop-up window must be hidden all time except when a singular motor is selected on HMI and close it again when operator pushes any button.
I´ve tried using frames and buttons inside it, but cannot find a way to hide the frame.
By now, I´m using Bitmap object as lower layer acting as a frame; Range of Text Images to show motor name, acting as frame title; and a couple of buttons, all above objects with hide bit.
Any other idea or suggestion?
-
Cara, I prefer Modbus either over RS485 or Ethernet, also UniCAN for remote I/O.
I would like having Ethernet/IP in Unitronics products
Timer not changing state...
in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Posted
As T8 is self-reseting, probably O8 never set. Try SET instruction to check if T8 is really doing what you want