micapp Posted October 18, 2011 Report Posted October 18, 2011 I have V570. It stops after 2-3 days with the following screen V290/V570 (T20B) O.S. (Stop Mode - Fatal error) 003.004.16 Aug 24 2011 17:12:29 Enum : 0x00000801 00000000 IP : 0x00300028 0002006E Ldr : 0x00000094 Desc: Illegal Word Operand Access Status Idle Is this meaningful?
R.Mozes Posted October 27, 2011 Report Posted October 27, 2011 Hi, SuchPLC reaction may occurs as a results of incompatibility system files versions. Pleaseuse the latest VisiLogic V9.3.1 (Download) Whenusing VisiLogic V9.3.1 (or any version) you must download all the system filesthat released with each version: · Boot · BinLib · O/S Usea COM port to download the BOOT and the BinLib. ***Avoid system incompatibility - Please note *** Thesystem files in V9.X.X are not compatible with V7.X.X or V8.X.X Makesure that you are using the O/S, BinLib, Boot that implement in each VisiLogicversion 1. Turn OFF the PLC and use it as standalone ( Disconnect I/Oexpansions ,Ethernet….) 2. Touch and hold the screen 3. Power ON while screen is touched 4. Touch twice in Bootstrap screen Makesure the Connection Settings are correct (COM PORT RS232 ONLY, 115200baud rate and 6sec time out) Pleasemake sure that you are using the latest system files (Go to help menu>updatefrom the web>operation system) Downloada blank application to the PLC by using PC's COM Port and PLC's COM1 RS232. Ifeverything is ok, try to download your application and let us know yourresults.
Damian Posted October 27, 2011 Report Posted October 27, 2011 I have had the same error in the past, and in my instance it was EMI related due to some grounding issues. Try going through the published Unitronics document regarding EMI and the measures to take to minimize its effect. You can download it at the very bottom of this link http://www.unitronics.com/Content.aspx?page=Technical_Library It can also generate that error with a bad connection on the snap in IO and well as a bad connection to expansion IO. The unfortunate thing is there are many different things that can cause that same exact error. It is best to just start with the most likely and address them one at a time until you rule them out.
John Williams Posted November 16, 2011 Report Posted November 16, 2011 I also have a problem with a V570 stopping due to Fatal Error and displays the following... V290/V570 (T20B) O.S. (Stop Mode - Fatal error) 003.004.16 Aug 24 2011 17:12:29 Enum : 0x00001110 IP : 0x000C7140 00077BDC Ldr : 0x000001DC Desc : Illegal Word Operand Access Status : Idle © Copyright by UNITRONICS I thought I had upgraded to VisiLogic V9.3.1 but not by the method described here. Must all upgrades be performed through the boot screen instead of the VisiLogic wizard? What types of grounding issues should I look for? Nothing in the EMI publication seems to point to a fault in the installation. All help welcome. Thank you.
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now