V1040 lost it's memory


Recommended Posts

I had a customer ring yesterday with an error on the screen:

Stop Mode Fatal Error

003.004.00

No Application

It seems that the PLC lost its memory while it was powered up and running. I haven't been backing the program up to flash for various reasons. Has anyone seen this before. I checked the battery and this was ok, not that it should matter because the PLC was powered up the whole time. I have seen PLC's get corrupt memory before but never lose there memory completely. What happens if the memory in the V1040 gets corrupt?

Link to comment
Share on other sites

  • 2 weeks later...
  • 1 year later...

We have had similar issues on a particular group of equipment we built using the V570-57-T20B and V200-18-E1B, a couple "no application" faults and several screen freezes to name a couple.  Because I, nor my co-worker, am not an EE or EET, what sort of test equipment can we use to test for noise or feedback?  Some of the units have had multiple occurances, others none at all (that I am aware).  Or alternatively, how can we better protect the PLC power & grounds as well as the inputs?

Link to comment
Share on other sites

  • MVP 2023

Eric-

 

If you've got a PLC loosing it's mind on an intermittent but regular basis I would strongly suspect electrical transients (spikes).  For starters, if you have any inductive loads connected to the outputs of the -E1B do you have surge suppressors across the coils?  While the relay outputs of the -E1B are isolated, I have seen the PLC go into error when something as seemingly trivial as releasing two small contactors at the same time.    

 

An inductive load always throws energy back into the system when you turn it off as the magnetic field collapses.  It will create a huge (>400V) spike across relay contacts which I guarantee will induce spikes in the other conductors on the board.  You need to give that spike some way to dissipate itself.  If you have AC coils, use RC snubbers.  For DC coils use a 1N4007 diode wired with the band to the positive side.  Put them as close to the inductor as possible.

 

To answer your question on test equipment, if you want to catch noise or spikes you need an oscilloscope, preferably one with digital storage and a one-shot mode.  Then start poking around on all wires connected to the PLC with the trigger set to 50V.

 

Joe T.

  • Upvote 1
Link to comment
Share on other sites

  • 2 weeks later...

Thank you Joe.  We have some of the outputs controlling resistor suppressed relay coils (generally 12vdc) and others are directly controlling the coils on 9W and 10W valves (also generally 12vdc).  The valve coils have no resistor or diode.  I am assuming that if we can only install the 1N4007 at the E1B, this would be "better than nothing".  Some instances this will be the only location to put the diode.  Other instances we would be able to put the diode within inches of the coil.

 

We do have a small digital storage scope with a 1x/10x probe.  Not sure if it has a "one shot" mode or not.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...

Important Information

This site uses cookies. By clicking I accept, you agree to their use.