Hello.

I am programing Unitronics V1210 with VisiLogic v.9.4.0.

The program I am working at, does suddenly not work as it should, when I touch the numeric displays with Keypad Entry, there I am supposed to change the numeric values, nothing happens, No keypad pop up.

And if I goes to the Information mode the password is requested, the password windows pops up but then nothing hapens, I cant type the password and cant escape.

I have puted in older version of my program that did work before, but now the same problem is there, the keypad window wil not appear, but It comes a little flash on the screen.

Is there a solution for this problem?

Posted

This is happened to me before on a V1040 and I ended up having to re-install the OS. A colleague of mine also had a similar problem as this and he ended up having to pull the Ethernet adapter out. Don't know if you are using ethernet but it might be worth a try.

Posted

Without seeing your application...just a shot in the dark...

I had a similar problem with a V570. Turns out I had an active "Show Alarm" function block, but there there was no alarm configured for the ID# specified, so it didn't appear on the screen. I could navigate through various screens no problem, but any fields/buttons that required pop-up keypads were not functional.

Dave

Posted

Hi,

It seems the applicaiton calls a display evey scan. Check that all the conditions for calling a display are with one shot condition.

As Dave mentioned also calling the alarm display (using Show alarm /shpw groups) should be activated with one shot condition.

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...

Important Information

This site uses cookies. By clicking I accept, you agree to their use.