VisiLogic missing IO modules


Recommended Posts

I am working with VisiLogic 9.8.31 and using a V570 controller. I am unable to find/load the following modules in HW Configuration: IO-D18-R08, EX-A2X, and V200-19-ET2. Is this an issue with outdated software? I just downloaded it a few weeks ago. 

I'm not sure if I need to be physically connected to the modules in order to recognise them. The actual PLC and modules haven't arrived yet, Just doing some initial setup. 

Any suggestions would be appreciated - this is my first time using Unitronics equipment and software.

Thanks!

Link to comment
Share on other sites

  • MVP 2023

There's no entry needed for the EX-A2X.  It's assumed you have one, as nothing works without it.

The V200-19-ET2 is the Ethernet Card.  This is initialized in the ladder logic - read the Help on Card Init.

The proper part number for the digital module is IO-DI8-R08.  This is in there.

Joe T.

  • Upvote 1
Link to comment
Share on other sites

Visilogic assumes that the EX-A2X is present if you are using expansion I/O, so you don't need to add it into the hardware config. 

The IO-DI8-RO8 is listed with the IO-DI8-TO8 and will show as IO-DI8-TO8/RO8 in the hardware config screen under I/O Expansions.

The V200-19-ET2 is a card that the PLC recognizes when you plug it in it's not part of the hardware config.  You do have to make sure that the card and sockets are initialized, and a PLC name is set in in the ladder(recommended to be done with SB2 on power up) in order to use the V200-19-ET2.

 

Joe beat me to it  :)

Edited by Cam
  • Upvote 1
Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...

Important Information

This site uses cookies. By clicking I accept, you agree to their use.