martin988 Posted November 24, 2017 Report Share Posted November 24, 2017 Hello , I am using the linearization block in Visilogic to control a current analog output with the following options: input MI from 600 to 1000 range ---- linearization-----> analog output from 819 to 4096 range My question is what value will the analog output have when the value of the input MI exceeds or drops bellow the range (600 - 1000)? I dont have a PLC right now, so i cant test. Thanks Quote Link to comment Share on other sites More sharing options...
MVP 2022 Ausman Posted November 24, 2017 MVP 2022 Report Share Posted November 24, 2017 Hi Martin, you need to have logic to cover this, using compares. It is something I have raised with the creators, trying to have max/min amounts incorporated into the block. No luck as yet. cheers, Aus Quote Link to comment Share on other sites More sharing options...
MVP 2022 Joe Tauser Posted November 25, 2017 MVP 2022 Report Share Posted November 25, 2017 What will happen when the input to the block is out of your range is it will continue to linearize as it should, going above and below your 819 and 4096 points in a linear fashion. What will happen with the analog output is it will continue down to zero mA on the low end and if you get above 4095 it will also go to zero mA. 7 hours ago, Ausman said: you need to have logic to cover this, using compares Yep. Joe T. Quote Link to comment Share on other sites More sharing options...