  • MVP 2023

There is an example of the Unitronics alarm manager under Help->Examples->Version 900 -> Project examples -> ladder -> V1040 Alarm Example.vlp.

The Unitronics alarm manager is a bit of a complicated beast for someone new to the product; you may be better off making your own alarm handler in logic depending on what your needs are.

Can you describe what you want to do?

Joe T.

Link to comment
Share on other sites

10 minutes ago, Joe Tauser said:

There is an example of the Unitronics alarm manager under Help->Examples->Version 900 -> Project examples -> ladder -> V1040 Alarm Example.vlp.

The Unitronics alarm manager is a bit of a complicated beast for someone new to the product; you may be better off making your own alarm handler in logic depending on what your needs are.

Can you describe what you want to do?

Joe T.

I need alarm screen on hmi , where i can find allarm history , and can i on unitronics do something like this : when alarm is activate example security circuit is broken down , i need pop up with message circuit is broken ?

i have one more question about indirect function on photo you can see my leader diagram 

http://pokit.org/get/?4e32ee4c563cefb6ee9722e39481ef5f.jpg

http://pokit.org/get/?63103df24bd0eacbb2befc9000babcf2.jpg

http://pokit.org/get/?0c66c4829007019b5e5e2c57421ae8e4.jpg

why dont load hmi screen when timers are on ?

you can see on photo 1 and 3 diagram on photo two are timers

one more questions here if you see on select day of month when i select 20 day day 1 is automatic on

why ???

 

 

Link to comment
Share on other sites

  • MVP 2023

The Alarm manager will do what you're asking - it's configured in the tree on the right in Visilogic.  Read all the Help on Alarms before you dive into it.

Photo 1 - you have the same register for Month and Day.  These should be different.  When you go online, what values do they contain?

Photo 2 - a very nice screen but I have no idea what's under the hood

Photo 3 - I don't see a timer.  That logic will call a display once, as the coil triggering the transition is hanging on the power rail.  Is the rail in a subroutine?  

Joe T.

Link to comment
Share on other sites

28 minutes ago, Joe Tauser said:

The Alarm manager will do what you're asking - it's configured in the tree on the right in Visilogic.  Read all the Help on Alarms before you dive into it.

Photo 1 - you have the same register for Month and Day.  These should be different.  When you go online, what values do they contain?

Photo 2 - a very nice screen but I have no idea what's under the hood

Photo 3 - I don't see a timer.  That logic will call a display once, as the coil triggering the transition is hanging on the power rail.  Is the rail in a subroutine?  

Joe T.

ok i make mistake on photo one , but i have this problem on photo one you can see day of month isnt on why ??? on photo two you see what i set on my plc 

on photo 3 are my definition of day of month

http://pokit.org/get/?f08eb856ab7f8cded373411b2a4ee7f5.jpg

http://pokit.org/get/?c44d1571d8c8a67db5deb6be38915e8b.jpg

http://pokit.org/get/?6c12be8aeb7494e0ae77edf287327d5e.jpg

 

 

 

Link to comment
Share on other sites

2 minutes ago, Joe Tauser said:

It's hard to troubleshoot a program without all the information.  What are the online values of MI 57, MI 58, ML 81, and ML 80?

Joe T.

M57 is time for "start  obavijesti" M58 is time for "Stop obavijesti"  ML81 is day of month and ML 80 is month 
i have only problem with days 

 

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...

Important Information

This site uses cookies. By clicking I accept, you agree to their use.