knltechpe Posted January 30, 2018 Report Share Posted January 30, 2018 Anyone ever have a problem trying to program an EX-RC1 in bridge mode over Ethernet? I have a v700 that is connected to three EX-RC1s. When I attempt to load new code to any of them using bridge mode, I'm getting a "retry binary transmit" message from Visilogic followed by an error 240. The download process then halts. Any insight would be appreciated. Regards, Mark Quote Link to comment Share on other sites More sharing options...
MVP 2022 Flex727 Posted January 30, 2018 MVP 2022 Report Share Posted January 30, 2018 Have you tried increasing your timeout parameters? Quote Link to comment Share on other sites More sharing options...
MVP 2022 Joe Tauser Posted January 31, 2018 MVP 2022 Report Share Posted January 31, 2018 That sounds like an issue with the integrity of the CANbus network installation. 1. Are you using real and true CANbus cable (Accept no substitutes! Or if you're like me and don't want to pay big bucks for the wire and use CAT5 instead, dial the baud rate down. This is NOT Unitronics' official position, but it does work for testing. Buy the real stuff when you ship it.) 2. Is it terminated with a 120 ohm resistor on each end? 3. Is the cabling daisy-chained or starred? Starring is bad. 4. What is the baud rate? Joe T. Quote Link to comment Share on other sites More sharing options...
knltechpe Posted February 5, 2018 Author Report Share Posted February 5, 2018 I tried increasing the timeouts and got some moderate improvements, but still saw these timeout errors. This was over Ethernet. When I connect to the USB port on the PLC and use bridge mode I can program all the EX-RC1s. The CANBUS cable is Belden 3084, which I believe is what Unitronics specified or used as an example in their data sheet. All devices are daisy-chained, with 120 ohm resistors at each end. Baud rate is 500K. I'm wondering if the ethernet switch I'm connecting through may be contributing to the problem. Mark Quote Link to comment Share on other sites More sharing options...
MVP 2022 Joe Tauser Posted February 6, 2018 MVP 2022 Report Share Posted February 6, 2018 You can connect directly to the PLC with an Ethernet cable. It will handle crossover detection. Joe T. Quote Link to comment Share on other sites More sharing options...
Recommended Posts
Join the conversation
You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.