Master and Slave at same time...


ORSO2001

Recommended Posts

Dear Alls,

I have to set up my Unistream to works at same time as Slave by Modbus RTU TCP and Masert by Modbus RTU RS485.

I already wrote the program part about slave (Modbus TCP) than I set PLC communications->Protocols->MODBUS->Slave->Panel Ethernet...I have set the registers and "wrote" the code...now I am approcing the Slave side...my question is:

I must use/set the same PLC communications->Protocols->MODBUS->Master->RS485 or I can mix/use the first with the PLC communications->Physical->Serial COM ?

I hope that my qestion is clear enough.

thanks

Link to comment
Share on other sites

ok...I found what I have to do....and also reading again my first post this has no sense...sorry usually I used unitronics as master using the "advanced modbus"...now I am trying to use "periodic/aperiodic" and at this point I have few questions:


- using "advanced modbus" if a data exchange don't works I use an instruction to empty the buffer to try again...using "periodic/aperiodic" this works automatically or I have to do something?


- when I compile the project I have a warning like: Do NOT place "COM: MODBUS" Ladder elements on the bus bar, or anywhere it will be continuously activated.
Use a delay of 10-50 msec between requests. Click on "Find All Elements" to locate all of the instances where it is used in the program
...I placed a "P" contact and a "modbus aperiodic trigger" to do some test...this warning is for safety or I am missing something?

thanks

Link to comment
Share on other sites

I also have that error- Do NOT place "COM: MODBUS" Ladder elements on the bus bar, or anywhere it will be continuously activated.
Use a delay of 10-50 msec between requests. Click on "Find All Elements" to locate all of the instances where it is used in the program

Also the command is not being called continuously (with a positive transition contact).

The program appears to work OK,but I still get this error at each download.

Any help would be appreciated

image.png.e32c7b0b22121f3568e276136ce8b793.png

Link to comment
Share on other sites

It is just a warning, ignore it. We cannot detect (unless the element is directory on bus bar) that it will be called continuously or not), since it  might be on a bus bar of another function that is called through a timer, or the other way around: not on bus bar, but after a Contact that is always open dues to the state of the connected bit.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...