Solvaer Posted July 11, 2018 Report Share Posted July 11, 2018 Hello, Im currently programming my plc for the next big project, and this time we are going to be using the samba 7 instead of the m90 which we have been using for the past 10 years. and i am running into a problem while trying to figure out how the counter system works. i want a counter to count once (rise) when my output O.1 rises. I have managed to make a counter that starts counting like crazy all the time that output is active. how do i change it to only rise once? Quote Link to comment Share on other sites More sharing options...
MVP 2022 Flex727 Posted July 11, 2018 MVP 2022 Report Share Posted July 11, 2018 Use a Positive Transition contact instead of a Direct Contact in front of your counter. 1 Quote Link to comment Share on other sites More sharing options...
Cam Posted July 11, 2018 Report Share Posted July 11, 2018 Use a positive transition contact -|P|- Quote Link to comment Share on other sites More sharing options...