jarflo240 Posted November 14, 2018 Report Share Posted November 14, 2018 Good afternoon: Please, I get this in the program and the input signals arrive but I can not see the software when I'm online. Quote Link to comment Share on other sites More sharing options...
Cam Posted November 14, 2018 Report Share Posted November 14, 2018 Are there forces in place on those inputs?? Quote Link to comment Share on other sites More sharing options...
MVP 2022 Ausman Posted November 14, 2018 MVP 2022 Report Share Posted November 14, 2018 Agree with Cam, it appears that you have forces in place. These are done when online by left click in the yellow area of the operand in the ladder, and then right click on the Set box in the little window that then opens. Right click brings up a choice of force options. Running forces can cause all sorts of odd issues and must be done carefully, not only in unitronics equipment but all plcs in general. Also, if the ladderwork is in a subroutine, ensure that you have actually called it. Visilogic has a major quirk/fault/problem in that it shows red colours (which imply active power) in routines that are NOT actually being called. cheers, Aus Quote Link to comment Share on other sites More sharing options...
jarflo240 Posted November 15, 2018 Author Report Share Posted November 15, 2018 THANKS Quote Link to comment Share on other sites More sharing options...