Viking Tool Posted March 21, 2019 Report Share Posted March 21, 2019 This is our first time looking and using a this PLC. I am very green. So forgive me. We attempted to link port #1 with the RS11 cable to Keyance DL-RS1A. Initiated port #1 in bit relay. Used the bit relay to open protocall scan. After doing that I can not get the PC to communicate to PLC. I am using Visalogic 9.8.65 & have been connecting PC to PLC with a serial cable. Someone please help me. Quote Link to comment Share on other sites More sharing options...
MVP 2022 kratmel Posted March 21, 2019 MVP 2022 Report Share Posted March 21, 2019 As i see it is Samba PLC. Maybe you use the port and protocol configuration wіthout SB2 contact. You must go to info mode and Stop PLC for make connection possible. Please post vlp with protocol config. Quote Link to comment Share on other sites More sharing options...
MVP 2022 Joe Tauser Posted March 22, 2019 MVP 2022 Report Share Posted March 22, 2019 Never use port 1 to communicate to external devices unless you've installed an Ethernet card so you can still get in. Buy another serial port and use COM 2 for this sort of thing or get an Ethernet card. Joe T. Quote Link to comment Share on other sites More sharing options...