MVP 2022 Flex727 Posted July 12, 2019 MVP 2022 Report Share Posted July 12, 2019 What is this parameter under Ethernet in INFO Mode? It can be changed but does not stick through a power cycle. Can it be set through ladder? Quote Link to comment Share on other sites More sharing options...
Isakovic Posted July 13, 2019 Report Share Posted July 13, 2019 I think it's time PLC waits to resend message after unsuccessful communication attempt. SI 101 is system register for TCP/IP time out. You should be able to set it from ladder. Quote Link to comment Share on other sites More sharing options...
MVP 2022 kratmel Posted July 13, 2019 MVP 2022 Report Share Posted July 13, 2019 SI 101 TCP/IP retries base time out Legal values are 1 to 10, units of 100 msec (1 stands for 100 msec etc.) Default value is 200 msec. Same value is for ALL 4 sockets Requires CARD INIT Illegal value request will be rejected (no change) Quote Link to comment Share on other sites More sharing options...
MVP 2022 Flex727 Posted July 13, 2019 Author MVP 2022 Report Share Posted July 13, 2019 Thank you! I'll give that a try. Quote Link to comment Share on other sites More sharing options...