vasovas Posted August 31, 2019 Report Share Posted August 31, 2019 Hi, guys, Can you please advise wiring diagram for PT100 3 wires sensor to SM35 J R20? Thank you! D.Vasilev Quote Link to comment Share on other sites More sharing options...
MVP 2022 kratmel Posted August 31, 2019 MVP 2022 Report Share Posted August 31, 2019 It is impossible for SM35 J R20. You need to use SM35 J RA22 or SM35 J TA22. Quote Link to comment Share on other sites More sharing options...
MVP 2022 Joe Tauser Posted September 1, 2019 MVP 2022 Report Share Posted September 1, 2019 As kratmel points out, the R20 doesn't have RTD inputs. The easiest thing to do would be to get an RTD / 4-20 mA converter and connect it to one of the R20's analog inputs. Google up "RTD transmitter". Joe T. Quote Link to comment Share on other sites More sharing options...
vasovas Posted September 1, 2019 Author Report Share Posted September 1, 2019 Thank you for your prompt replies, guys! I will try what Joe Tauser advises. D.Vasilev Quote Link to comment Share on other sites More sharing options...