  • MVP 2022
This module is somewhat unique in that the analog outputs have an option for +/- 10V instead of the normal 0-10V. The spec sheet says:
Quote
Resolution (except at 4-20mA)   12-bit (4096 units) + sign
This is not clear to me. Does this mean that the operand should range from -4095 to +4095 to output -10V to +10V, or does it mean -2048 to +2047? I suspect the latter (I guess it could be -2047 to +2048).
I guess there is one other possibility. It could be 0-4095 to cover the range -10V to +10V. In this case, the range I would be looking for with a 0-10V output would be 2048-4095?
It would be really nice if Unitronics had spec sheets that were a little more clear. Especially in this case, as it would be important to know what value corresponds to 0V.
  • MVP 2022
IO-AI4-AO2                                        Input
                                                         Output
12 bit   (0-10V, 0-20mA,
4-20mA)
12 bit +sign ( ±10V, 0-20mA,
4-20mA)
0-4095, 4096 units (except at 4-20mA)
819 to 4095, 3277 units (at 4-20mA)
0-+4095(except at4-20mA)
  • MVP 2022
44 minutes ago, kratmel said:
Two IO-AI4-AO2 modules are installed in my laboratory.  I'm trying to check it out tomorrow.
Thank you! I do not have one these modules and my first opportunity to test will be on a customer installation during commissioning. I'd rather not find out it's wrong at that point. They're less than $200, but I rather not spend the money if I can avoid it.