Mac9010 Posted February 7 Report Share Posted February 7 Hello everyone I have a problem with a program, the situation is the next, When there is a sudden power outage my plc shuts down but when it is reset it does not retain the setpoint values that were previously loaded. I have already checked if the values are retained and indeed if they are retained Cold you give some advice or tell me what can I do to solve this issue? the cpu is USP-070-B10/B and the software is the next. Thanks in advance. Quote Link to comment Share on other sites More sharing options...
Gabriel Franco Posted February 7 Report Share Posted February 7 Is the battery installed?, is it good? Quote Link to comment Share on other sites More sharing options...
MVP 2021 kratmel Posted February 7 MVP 2021 Report Share Posted February 7 Is it CPU-for-Panel present? Panel cannot operate independently. CPU-for-Panel must be plugged into the back of a UniStream® HMI panel. The panel provides the CPU’s power source. The CPU-for-Panel comprises: 1 IO/COM Bus connector for interfacing Uni-I/O™ & Uni-COM™ modules 2 Isolated RS485 and CANbus ports3 Backup battery Quote Link to comment Share on other sites More sharing options...
ORSO2001 Posted February 8 Report Share Posted February 8 hi Mac9010 for what I saw from your programa all seems ok...maybe, as already suggested, the battery is low and the retained memory is not save...is the "time date" ok at every reboot? Quote Link to comment Share on other sites More sharing options...
Mac9010 Posted February 10 Author Report Share Posted February 10 Hi everyone, thanks for your advices. I solved the problem, I change the battery. The battery didn't voltage . Quote Link to comment Share on other sites More sharing options...