Jhav Posted April 24 Report Share Posted April 24 Hello, I was wondering if there is a simple way of using one timer for multiple inputs. I have multiple valves and each one has a open input and a closed input . I’m allowing a couple seconds between status change of open and close if it does not reach the right position the valve will alarm. Is there a simple way of using one timer for all inputs instead of giving each individual input a timer? Quote Link to comment Share on other sites More sharing options...
MVP 2021 Joe Tauser Posted April 24 MVP 2021 Report Share Posted April 24 It is tedious, but the generally accepted way is to assign one timer per valve. If you don't use multiple timers you won't know which one failed. Joe T. Quote Link to comment Share on other sites More sharing options...
Jhav Posted April 24 Author Report Share Posted April 24 thank you Joe. it looks like I need to start making some timers. Quote Link to comment Share on other sites More sharing options...
MVP 2021 kratmel Posted April 24 MVP 2021 Report Share Posted April 24 12 hours ago, Jhav said: I was wondering if there is a simple way of using one timer for multiple inputs. This is another way - try to configure standard Alarms with configured delay. You do not specify PLC model but 16 to 128 Alarms can be configured with different delay. Quote Link to comment Share on other sites More sharing options...