Irfan Posted August 12, 2023 Report Posted August 12, 2023 Sir ,I am facing problem in Analogue input Some channel getting value and some Channel not get any value I am using 4-20mA 10 bit A0 getting value but A1 not getting any value A2 getting value but A3 not getting any value Please inform me reason
MVP 2023 Joe Tauser Posted August 12, 2023 MVP 2023 Report Posted August 12, 2023 Moved to the correct forum. For a 4-20 mA signal, do you have the jumpers set properly inside the module? If so, remove the input signal and measure the resistance between the input terminal and the COM terminal. It should be 500 ohms. I've been known to connect 24VDC directly to a 4/20 analog input and frying the resistor. Joe T.
Irfan Posted August 12, 2023 Author Report Posted August 12, 2023 Thanks for reply I have tasted with current injector.jumper setting also correct. A0 A1 Com. A2 A3 Com A4 A5 Com. My sensor connected all channel and getting value A0,A2,A4. I am using CPU V200 with Ex module
MVP 2023 Ausman Posted August 12, 2023 MVP 2023 Report Posted August 12, 2023 If you swap your inputs around what happens? ie A0 and A1 swapped. cheers, Aus