Some tips:

1) You must start to use UMI via blank project and configure 1 VFD.  

2) Configured Umi can be controled via simple UMI command (from UMI menu) and by changing speed and torqe variables defined in configuration.

3) Is it dip sw on RS485 comm card in correct = RS485 + termination?

4) Is it cable from UMI to RS485 card connected properly?

 

P.S.  I do not find any UMI inverters on din rail in Visilogic HW config of your project.

ADD UMI to project = add some hidden subroutine that is not visible for user.

You must try start to use UMI via project from example for configure 1 VFD.  

Link to comment
Share on other sites

4 hours ago, kratmel said:

Some tips:

1) You must start to use UMI via blank project and configure 1 VFD.  

2) Configured Umi can be controled via simple UMI command (from UMI menu) and by changing speed and torqe variables defined in configuration.

3) Is it dip sw on RS485 comm card in correct = RS485 + termination?

4) Is it cable from UMI to RS485 card connected properly?

 

P.S.  I do not find any UMI inverters on din rail in Visilogic HW config of your project.

ADD UMI to project = add some hidden subroutine that is not visible for user.

You must try start to use UMI via project from example for configure 1 VFD.  

Greeatings , i dont use umi , i Have 3 vfds , and samba can only with 2 , 

Dip switch are 1 2 3 4 are on and the 5 6 OFF

I get cable form unitronics two wire one blue and it is on pin 1 and bluewhite it is pin 6 ,

1 pin +Rs485 on VFD

6pin -RS485 on VFD

 

have you any other solution

Link to comment
Share on other sites

  • MVP 2023
3 hours ago, t0r3r0s said:

have you any other solution

You must post VFD model # and (or) VFD communication manual.

All of  VFD must be configured before connect to any communication (network ID, comm speed, start command source and speed command source must be defined).

After that you must use PC Modbus software (and USB-RS485 dongle) for test communication and VFD operation. Only after success with this step you can try to set VFD - PLC communication.

 

Link to comment
Share on other sites

Hi;

 

A Note from Experience.

A SAMBA PLC has Limited Memory !!

When Adding  Unitronics VFD   Functon blocks  to a SAMBA, it takes up a lot of that available memory and leaves only a small amount for actual application programming.

User program will have to be very small.

( In our case, customer ended up using Small UniStream PLC   to handle the program and the VFD)

 

DanT

 

 

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...