I am using the example project provided in Unilogic for flow totalizing and everything proves out except the low end of my Linear conversion is still passing data.  20 mA (1023) passes 200gpm, and half signal, 12 mA passes 100gpm with no issues. 

image.png.d1a4d515a3f906f5de515cbd15302e30.png

4 mA should pass 0; but I am still getting data to my "Total gallons per minute", when I put 1-4mA through with my Fluke signal generator. This seems to defy logic as 0-4mA should not be passed!

Any ideas on this?  

 

Link to comment
Share on other sites

  • MVP 2023

And Van, welcome.  FYI, the program you are using is Visilogic, not Unilogic.  Just letting you know, as incorrect referencing could cause confusion because it is a totally different system from Unitronics.

Kratmel's answer is the solution, but the reason as such is that Linearisation will continue to do it's instructed outputs if input parameters go outside the supposed maximum or minimum.  this is especially confusing if using 4-20ma inputs.

You may also like to get this to help with your learning:

https://forum.unitronics.com/topic/3540-linearization-calculator-for-all/

cheers, Aus

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...