SM43JR20 flow meter project


Recommended Posts

I am using the example project provided in Unilogic for flow totalizing and everything proves out except the low end of my Linear conversion is still passing data.  20 mA (1023) passes 200gpm, and half signal, 12 mA passes 100gpm with no issues. 

image.png.d1a4d515a3f906f5de515cbd15302e30.png

4 mA should pass 0; but I am still getting data to my "Total gallons per minute", when I put 1-4mA through with my Fluke signal generator. This seems to defy logic as 0-4mA should not be passed!

Any ideas on this?  

 

Link to comment
Share on other sites

  • MVP 2023

Try simple solution - add net with Compare FB

If MI2 < 204   then MI3=0;

If MI2 >=204 and MI2<=1023 then use Linearization FB (you use it in net4) ;

If MI2>1023 then MI3=200

Last net MI3 stored to DW1

Link to comment
Share on other sites

  • MVP 2023

And Van, welcome.  FYI, the program you are using is Visilogic, not Unilogic.  Just letting you know, as incorrect referencing could cause confusion because it is a totally different system from Unitronics.

Kratmel's answer is the solution, but the reason as such is that Linearisation will continue to do it's instructed outputs if input parameters go outside the supposed maximum or minimum.  this is especially confusing if using 4-20ma inputs.

You may also like to get this to help with your learning:

https://forum.unitronics.com/topic/3540-linearization-calculator-for-all/

cheers, Aus

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...

Important Information

This site uses cookies. By clicking I accept, you agree to their use.