Thanks Saragani
What I have found that if I download a blank program to an V1040 that has had a previous program, that many of the MB values show 1 on the online view (even though there is no program in the PLC)
This is normally not a problem as when the MB is used in the ladder, after the first scan the value is set to 1 or 0 according to the program.
However if this MB is just linked to a button for jumping to another display and is not referenced in the ladder, I see that the MB stays at 1, causing unpredictable jumps.
As soon as I use a different MB the problem is solved.
Hope this clarifies the problem.
Regards
Denis