  1. Benito, the direct answer to your question is NO. 

    If I try with the programming tool, the PLC hangs.
    23 hours ago, Ausman said:

    It will start, but then fails and the plc is left in limbo.

    But....you can get around this issue by having an onsite PC with serial port as an intermediary connection.  Your factory floor people could have a laptop they carry round, they plug in the serial connection and you do the rest by accessing the PC via wifi using a VNC.

    Please also have a look at this topic to get an understanding of what Flex is saying:

    https://forum.unitronics.com/topic/7245-dont-update-just-because-you-can/

     

    • Like 1
  2. With your PLC being a 130, I respectfully disagree with Flex saying you can update firmware by ethernet.  Software yes, Firmware no. 

    As far as I know, unlike higher level Vision controllers, you cannot update a 130's OS via ethernet, it has to be done via the serial port.  It will start, but then fails and the plc is left in limbo.  To do this is not a usb cable, it needs a proper serial port on the PC using the correct PLC adapter and cable.  If the PC serial port is achieved using a usb to 232 adapter, the adapter has to be based on a Prolific chip. 

    As for your 130s losing OS, I would be looking at two things.

    1).  Electrical interference.   Shielding and correct elimination of spikes from coils, contactors etc has to be done.

    2).  If you already have ethernet connections to the 130s and they are accessible from the internet, then I would immediately change the default port(s) to something else.  It is very possible that what you are experiencing is due to hacking attempts.  If you can do so, update to the latest Visilogic version for better security and be prepared that you might need to change your program a little due to the upgrade.

    cheers, Aus

     

    • Like 1
  3. The Help system is your friend, along with doing simple trial and error learning.  To fully understand something new, work on that one concept alone as a project until you fully understand how it works and can then relate it to your other needs.

    At present I would also have a good read of everything HMI related in Help, and also some other things that are important to know with regards to how the scan proceeds and can actually take a few scans to settle HMIs, in Program Sequencing: Modules, Subroutines, Labels & Jumps. (copy that into Search and it should be the 2nd topic). With single calls it is very easy to muck things up if other ladder elements have not got to where you think  they are!  Sometimes a relocation in the ladder is all that is needed.  I often use a Negative Transition Contact for using the physical button pushes on 130s (ie no touch screen) and this inherent delay is useful.

    Everyday you learn something new.

    cheers, Aus

    • Like 1
  4. Perhaps it would be useful at present to try and monitor the strings, change things and find the successful resolution by using a PC, like I often suggest for getting around modbus 485 issues. 

    It is far easier to manipulate strings/sends etc on the PC, and then once the correct one is found for what is wanted, transfer it to the PLC. 

    I am likely showing my ignorance as I don't use can-open, but I know you can get usb canbus converters that can then be monitored easily, and a quick goggggles showed many programs available.  Perhaps there are other easier methods as well....but I would think that you at least need an actual interface/device on the PC.   Can you use a native serial port somehow?  I don't know.

    cheers, Aus

     

  5. Sorry, I missed that you had already said "burned".

    re Latest version, updating might  upset an existing program's operation.  I'd stick with the version you made your project on, until you iron out what your issue is.

    In the bottom left of the Visilogic window you can usually see progress through the download.  Is this actually happening?  It shows the type of connection, name of unit, and % progress etc.

    How are you doing the connection?    Cables DO fail for no reason.  If serial, on the PC are you using a usb converter or a native com port? And if serial have you tried another cable and adapter?

    cheers, Aus

     

  6. Doesn't the 8 character rule apply to everything on the SD?   Which in this case means the file name is too large and the PLC won't play?

    Quote from Help:

    Note ♦    Note that the main EXCEL folder and subfolders EXCEL0, EXCEL1, EXCEL2, EXCEL3 can each contain 64 files, for a total of 320 .csv files.
                ♦    The .csv file name cannot exceed 8 characters. It may include only English characters and numbers: 0 - 9, A - Z, a - z, and the underscore character "_".

    cheers, Aus

  7. Others who know 350s might know the answer to your final observations/questions.

    Perhaps you are doing something wrong with the sequence of things.  But it still could be a faulty unit.

    I think official support should be involved and can do a remote session for you, submit a ticket. 

    https://support.unitronics.com/index.php?/ticket/submit-ticket

    And an aside......Another forum member contacted me directly and politely pointed out they never have trouble with OS updates regardless of what methods are used etc.  I can only relate my experiences of occasional issues and solutions I've found that worked for me.  Note that I only use 130s which can only be updated via serial.

    cheers, Aus

  8. No to a teamviewer session for me.

    Some last things to try but I think you're in trouble.

    1). Did you do the connection with W10 or W7?  In my W10 "upset" I could not write the boot files which previously I could.  W7 worked.  There are parts of the transfer that are done in a special way, which is why the prolific chip is needed along with other PC bits working as planned.  Somehow a W10 update on my PC corrupted this.  (I could not find the reason with quick looking and haven't had time to fully explore)

    2).  Remove the battery, wait a minute and replace with definite new.

    3). Force your comms to run at a slower speed, by setting both the PLC and PC rates to 9600.  The PC end is done by using device manager and selecting the port and then Port Settings.  And while you're there, check that the other settings are 8, None, 1, None.  Then in Visilogic set the same speed in the Communication window that you already know.  After doing all this, try again.

    cheers, Aus

  9. 17 hours ago, Ondrej Fedorcak said:

    Is it possible remotely?

    Highly likely.  However....

    I think a repeat of a previous mention is needed here.  How complex is the machine?  How many parameters? What did the parameters do?  How were they entered?  Via screen?  Optimised by machine usage itself from basic starting amounts?.......but the answer is likely "no" given you had trouble due to battery die.  Entered by being online with Visilogic?  

    These things are important.  You might be chasing your tail for no real reason if it is all fairly simple.

    cheers, Aus

  10. 16 minutes ago, John77 said:

    You mean finding a computer that allows me to connect the cable directly without an adapter?

    Yes, many on the forum have (cheap) older laptops specifically for this reason.

    Also, I found this on the Keyspan site:

    The USA-19HS uses a Texas Instruments/TI chipset.

    This might be the issue.  You need to use a Prolific based converter.  I don't know if the TI chip works or not.

    If you can use a PC with a native com port, if it doesn't work using W10, try to use it with W7 if possible.  W10 on my systems upset some serial stuff a while back.

    cheers, Aus

  11. And I also agree with Gabriel's interpretation.  "together in a Write Multiple Registers command"

    However, I do find this manual a bit confusing, given I can't find setpoint setting in any of these commands : Commands can be issued to the Alicat device using Modbus register1000. Commands are described in the table below. Some commands require a parameter to be passed in Command Argument register 1001 using the “Write Multiple Registers” Modbus function code.

    But then we also get to the legacy stuff at the end, so perhaps you should be trying register 24.  Look in 2.1

    So with all this confusing info, I still reckon your easiest avenue at present is using the PC.  I always start with a new device on the PC, and often find contrary things which take some time to figure out, along with other registers which have no reference in the manual but actually contain useful stuff.  It can be a "fun" game stepping through registers as a first try at a block of 10 and see if it reads ok, or then go to one by one.

    cheers, Aus

  12. I was at the homewares shop buying a new sofa for my loungeroom. 

    The salesman said, "This will fit four people without any problems."

    "Where am I going to find 4 people without any problems?"

    --------------------------------------------------------------------------------

    I took my cat's medicine by accident.  Don't ask meow.

    --------------------------------------------------------------------------------

    Paul and Joyce were at a marriage guidance meeting, and the counsellor told them that 80 percent of couples were so disconnected that the husband didn't even know their wife's favourite flower.

    Paul pondered this, looked at Joyce and whispered, "It's self-raising, isn't it?"

    --------------------------------------------------------------------------------

    and yes, there'll be more.........   🙃

    • Haha 1
  13. So...just a follow up on this odd behaviour.

    I discovered a topic already existed on the forum here:

    https://forum.unitronics.com/topic/1747-visilogic-94-invalid-bands-collection-index/

    There is mention of deleting the folder in C:\Users\YOUR_USER_NAME\AppData\Local\VirtualStore\Program Files (x86)\Unitronics, but in my case the only entries in this folder relate to Remote Access.

    So I tried the initial suggestion which relates to the .lyt file which is in C:\Program Files (x86)\Unitronics\Unitronics VisiLogic_C2\Main\Layout.  (Note the _C2 added for the instance in question) Added old to the name for safe keeping and copied the same file over from one of other instances.  I didn't use the one Cara has a link to as the size mismatched significantly.

    The faulty instance booted up ok, but needed direction to the project that I was initially using.  Once there everything is fine.  I haven't had any other errors appear (so far.... fingers crossed) like others mentioned in the earlier topic.

    Of special interest is what I discovered about the .lyt file upon closer inspection.  Opening the good file in Notepad++ brings up multiple lines of code up to 1672, but opening the dud one and it only has ONE line of code that is all NULS.  So somewhere in proceedings the file has obviously been significantly corrupted.  I can't really explain this, I don't believe I bit the byte gods that day (readers can now laugh at my little pun), and I don't recall any other odd things going on.  Both drives in the puter in question are good name, young SSDs and smart shows no errors or reallocations have taken place since new.  As already mentioned, caching is disabled as well.

    Something to ponder, but not too long for, unless it happens again.

    cheers, Aus

     

     

  14. 7 hours ago, Flex727 said:

    If you want the button to behave the way it does in VisiLogic, then you Set the operand on press and Reset the operand on release.

    All fair enough, but doesn't your explanation mean that it is on for a number of scans matched to the length of button push? Which is what Joel is doing ..........

    On 2/13/2024 at 1:58 AM, Joel Page said:

    an action that sets a bit on the pressed event and reset the same bit on the release action.

    And that was why I suggested the possibility of repeats each scan messing something up. 

    cheers, Aus

×
×