Posts posted by DanT

  1. Hi;

       "Yes, I have a copy that was saved which is what I attached, so that supposedly is the same as the one currently loaded "

     

    Use   Info Mode to look at the program name  that was last loaded  

             Touch any spot on the screen ( Not used for a programmed Touch action)   for  8-10 seconds

             Info Mode   ( Password   1111 )    Version,   Software  Project Name

     

    DanT

    • Like 1
  2. Hi;

    The V350-35-T2   has 1 Com Port  and a USB port for programming.   -- They both share the Same port - Port 1.

            Programming, Online Monitoring  and RS485 Modbus through this port will be a challenge for troubleshooting and programming.

     

    I will recommend using a 2nd   Com Port for the RS485 communications   -- V100-17-RS4X ( isolated RS485)

         Then you will be able to go online and monitor the communications with the drives thru the programming port - Com 1.

        The cost of the module  will pay for itself in reducing time and effort.

      DanT

  3. Hi ;

    What is the PLC Model?

    Do you know what version of VisiLogic was used to program the PLC?

         Older Versions are still available for download and use.

       If you do not know what version was used.

              Get the OS  Information   from   Info Mode, or    Connection - Get OPLC Information

                     Ask   Support@Unitroncisplc.com  what Version of   VisiLogic was probably used. - obtain it and install it.

                                Modify the program ( Original that you worked from  -- NOT the new   one you just did - will not be compatible)

     

    DanT

     

             

     

  4. Hi;

     

    The EX-RC1   is a Vision Product.

    Download     VisiLogic.

    Use VisiLogic to communicate with the EX-RC1  via the Serial Poert  ( 57,600 K )   ( RS232-CB1 COM Cable)

    The EX-RC1  is based around  a stripped down  V120 , set up for CANBUS communications.

    You can upload the configuration, save it and download to the new one.

    Remember to set the DIP Switches for the address.

    Check the configuration after you download and the structs  for the data transfers.

    DanT

  5. Hi;

    U90 ladder is the program to use with all M90/91  PLC's and JAZZ Series

    You can upload the program from the PLC  

         If the Prpgram is password protected, you enter the password.

     

    Start by making sure you can communicate  with the PLC using the    RS232-CB1 Com Cable  + a USB to Serial Adapter if necessary.

    Default Baud rate is 9600

    Controller

          M90  OPLC   Settings

                 Get Version   -- This will retrun info about the PLC you are connected   ( else you get a Com Error message)

     

    If Successfull,   Now

         Controller        Upload   -- to get the program into your computer.       -- Save it right away before trying to modify the program.

     

       DanT

     

  6. Hi;

    As pointed out above, Data Collection is possible using the Data Tables  you can create.

    Note the following:       V120 Series is an older series.     NO   Ethernet Option, NO  Micro SD Card  Slot

                                                      Getting the data out of the V120 will have to be done via the RS232/RS485   Com Port - Serial.

     

    Upgrade                               V130-J-TR2      -- Ethernet Option (V100-17-ET2) ,     Micro SD Card Slot,   ability to use the   SD Card Utility program.

                                                     or any other  Vision Enchanced Mode  OPLC l(V350, V430, etc)

     

     SAMBA Series can be used if the data is limited and the program not complex - SAMBA has Severe memory imits, and No Micro SD Card Slot, but   Ethernet (V100-17-ET2)  is an option.  SAMBA  has No Options for additional I/O.        ( Remote I/O can be considered, but at the expense of the limited internal memory you will be left with to use)

                                  

    DanT

                                                              

     

    • Thanks 1
    • Upvote 1
  7. Hi;

      I see the note about   MB 0 being set by  SB2, 

       Are these nets in a subroute?  Is the subroutine being called?

       If not sure -  put a Incremental counter ( XI whatever)    at the top of the subroutine- attached to the rail.

            If it counts, the routine is /was  active.  If not counting, subroutine ius not currently being called.

    DanT

  8. Hi Surg;

     

    Are the Tablet ( wireless)  and the USC PLC on the same network?     The VNC should be direct  connection.

    Another option is a P C  with Monitor  or a Laptop on the  same network - VNC will be a direct connection.

     

    If the Tablet and USC are on different networks, then you have to to go thru the customer IT to get it set up.

    Yes, UniCloud is another Option - you can use a Starter Subscription -  and also have some data in the Cloud.

     

    DanT

     

     

     

  9. Hi;

    Math required  for scaling.

    In Hardware config, choose an analog Input on the  V200-18-E4/4XB

           0-10V  Input       ( there is no   0-5 V )

          Select an   MI to Store the raw value.

     

          In the ladder      us the Linearize function     Scale the Analog Output based on   0-10 V Input

                    X Axis       0 to      16384    (   14 Bit Analog Input   -- 0 -1 0  V )                

                    Y Axis       0  to   222         ( 0-100  PSI    100/45  x 100   )   If you want  0.1  PSI Resolution    2220

          Test from there

                  

       DanT

  10. Hi;

     

    I reviewed the program.

     

    You are not properly triggering the Modbus   Read

    The  Tag  TAGASITEMP  is set up as both the data Tag and the Trigger -- will not work.

      Change the trigger name  to ( say)   TAGASITEMP-TRIGGER     in the Active Periodic  loaction 

        then in the ladder turn that    Bit   ON  to read the coil data   each time you want to   read the coil.

     

    DanT

     

    • Thanks 1
  11. Hi;

     

    In the Unitroncis Vision PLC, all the  MB's (Memory Bits)     and MI's  ( Memory integers ) used   are accessable by Modbus Reads and Writes.

       MB's  are Modbus Coils              MB3150     is Modbus Coil    3160

       MI's  are Modbus Registers      MI 100        is Modbus Register   100

    For efficiency of Modbus Reads and Writes, the programmer will probably lump   MB's and MI's  in groups that they know will be  Sent or Read by Modbus commands.

    Getting the Com Parameters

           Ask the supplier of the PLC.

    OR

    The way of checking for the Com Parameters  is via the Info Mode.

          On a touch screen PLC, press an area of the screen not activly used for touch for about  6-9 seconds.

                  Enter Info Mode     -- Password 1111

                      Choose Serial or Ethernet    and explore.

     

    DanT

  12. Hi;

     

    What PLC are you going to use it with ?

     JAZZ    or  SAMBA Series -- NO, they are not expandable

     Vision Series    -- OK  -- And you need the EX-A2X  as Alex has pointed out.

    UniStream Series   --   These will need an EX-RC1  and a CANBUS Adapter Module.

          There are UniStream Equivalents  if it is  for UniStream Series.   -- Let us know the Model PLC so we can recommend the proper adapter cable

     

    DanT

  13. Hi;

    Since UniLogic will not support anything Python, here are 2 possible methods:

           UniLogic Supports Modbus  Protocol

                              You can get Modbus Libraries for Python

     

            Unitronics has a feature called Message Composer  -- you can create text based messaged with variables 

                       Create  messages in Python and in  UniLogic to exchange data.

                      Get the UniLogic Example Programs Zip file.

                                        Under Communications - Protocol  there are some example to give you ideas.

     

    DanT

        

  14. Hi;

    You probably solved the issue by now, but  ( and for others ) :

    In VisiLogic,  :  Open        Connection  and       Get OPLC Information  ( Make sure you are communication with the PLC )

    When that answers back correctly,  Click   on the  Middle ICON     in the Communication - PC Settings Box  -- Yellow Sun with Red Dot

    Install Operating System      Click on Check   and follow the prompts,  

    The process may decide to install just 1 file, of maybe all 4 files.   

    Just click and let it do it's work  -- takes several minutes.       There is a progress bas that shows what is happening

    When done, it lets you know, Then reset and download your program.

     

    DanT

  15. Hi;

    Have you reviewed how VisiLogic  Handles Modbus register addressing?

    MODBUS Help is hard to Find in Help, but start here:   ( there is a lot of info there- just well hidden )

                                                                      Help, Index,   MODBUS

      Find and look at Slave Addressing.  Notice the SAMBA ( Vision Color) addressing is  set up in HEX ( Base 16)

         Know how to convert  Decimal to Hex and   back   -- Unitronics will do it automatic , but beware !

              in the example illustrated     7028  is Hex  0x7028     =   28712 decimal

         So is  8320   Decimal or Hex?          8320 Decimal =   0x2080 ( H-2080)

                                                                                    0x8320 Hex      =     -31968 decimal    ( MI's are Integers  +/-  32767)

       Just something to consider

    DanT

     

  16. Hi

    Are the other 2 PLC's Unitronics PLC's ?

          If they are connected by RS 485, the use Modbus  to collect the data

                     Each PLC must have a Unique Address      1   2   3   etc.

          If they are connected by Ethernet, use Modbus TCP

         Check  Help - Examples, Projects - Communications for example programs on how to do this.

     

    If they are not Unitronics PLC's, do they support Modbus Protocol?

          If they are connected by RS 485, the use Modbus  to collect the data.

                      Each PLC must have a Unique Address      1   2   3   etc.

          If they are connected by Ethernet, use Modbus TCP

     

    Once the connections are made, you get the data from the PLC's and store the data  in the V700  ( MI's)

         and then display the data  on the screen.

     

    DanT

×
×