  1. Hi;

    How fast are the inputs counting?  What is the Pulse duration?

    Input 8 and Input 9 are NOT  meant to be High Speed Counters.

          ( True  - they can be used for Very Slow Counting applications with long input signals)

    Inputs 0-1, 2-3, 3-4   ARE the High Speed Inputs.  These Inputs can be Normal Inputs  OR High Speed Inputs

    High Speed Inputs are set up in the Hardware Configuration.

    Look in Help   -- High Speed Counters   - to see how to set them up and the explanation of each option available.

    Change you wiring to the High Speed Counter Inputs.

    Also review the Installation Sheet  provided with the PLC.

     

    DanT

  2. Hi;

      In the Ribbon  starting with   Boolean, go to the end and under FB's  there is  Protocol

    Protocol is a method to compose messages to be send or received over the Serial Port.

    You can create simple or complex messages depending on the device you are communicating with and it's

       methods of  sending and receiving messages.

    You can also receive and decode the messages  from the device.

    Variables ( MI's, MB's, and others ) can be inserted or extracted from the messages.

    Review the Help   for Protocol, and the Example programs ( Help - Examples - Communications - FB Protocols )

    to learn how to effectively use this function.

     

    DanT

     

     

     

         

  3. Hi;

    The issue may be the OS in the PLC is newer than the Version of UniLogic you are using. ( example - OS in PLC is  from 1.31.116, and you are using  1.26.90)

       Program version, UniStream Version, and PLC OS Version must ALL be in synch.

       ( Not like VisiLogic where a Newer OS in the PLC can accept an older program from an earlier version)

    Check the OS in the PLC against the Version that UniStream has in it to install to the PLC.

    2 Choices:  --  Load  the OS from 1.26.90 onto a USB and install it into the PLC ( May have to force the install)

                             --   Upgrade UniStream to latest version and install the latest OS into the PLC and Upgrade your program.

    DanT 

  4. Hi Goldic;

     

    What PLC are you Using? - Only 1 Comport?

    If you can install the 2nd COM Port and use it to Communicate with your devices, then  it will be so much easier for troubleshooting - worth the money.

    Having the 2 com ports allows you to monitor the device communications a lot better.

    If your PLC has Ethernet Port Installed, then Use Ethernet for Programming and Com 1 for Devices.

    DanT

  5. Hi;

    V120-22-UA2  is actually 500Hz PWM  Max.

    PWM output is 24 V, PNP,  so it is Limited  -- also slow for a servo input, and wire the Servo Input accordingly

    PWM freqency   is  xxx.x Hz   500 Hz    is set as    5000  (500.0  Implied decimal)

    PWM Duty Cycle  is  xx.x%         50%     is set as    500 ( 50.0 implied decimal)

    If you have an oscilloscope available - look at  the waveform, especially if you want to push it above 500Hz !

    You will have to use a counter to control the pulses and turn the PWM   On and OFF.

    The V120 is an older unit and was not designed to really work with a servo.

     

    The V130-J-TR20  has better PWM High Speed Outputs  - NPN - 200kHz,  also some functions for basic servo control.

    If you also need the Analog Outputs, then the V130-J-TRA22 - NPN 200kHz.  The TRA has some functions for Servo Control.

    DanT

     

  6. Hi;

     

    The Sensor is PT-100  and will NOT interface directly to the  USC-B10-TR22.

    You can add the  UIS-04PTN   PT-100 Module,  or find a way to communicate with the  USB-PT-104   they supply.

    ( I do not see an English version of the documentation)

     

    DanT

  7. Hi;

    The V120-22-UA2  has 2 Comports.

    Use COM1  for Programming and Online troubleshooting.

    Configure COM2  for RS485 ( See Instruction Sheet for Jumpers to Set)

    You can use MODBUS to move Data between the units. Just watch the timing , Search    MODBUS    in the forum

    and there are several vey helpful  topics  by the experts about good practice in timing Modbus  Calls.

     

    DanT

     

     

  8. Hi;

     

    V120  Series cannot do Ethernet.

    Look at the V130-J-TA24  + V100-17-ET2 ( Ethernet Card)       LCD Screen, Keypad

    or

                              V350-J-TA24 + V100-17-ET2 ( Ethernet Card)      3.5 inch Colour Touch  HMI

    If the program is small and compact, look at the SAMBA  Series

    VisiLogic has methods to convert existing  program from V120 to V130 or V350 Color - Ladder OK, then Modify the screens

    Also look at the  Software Developer Tools under the Visilogic downloads  for .NET drivers and Active X tools.

     

    DanT

  9. Hi;

     

    Have you checked out the examples under Help, Sample U90 - Modbus.

    Also Check Help  -- MODBUS  -- Copy to Google for Translation   if a Help Version is not available in your language.

    Also Look at   --  Special Functions  --  Modbus Commands are done as Special Functions using registers(SI's)  

    U90 Ladder does NOT HAVE function blocks like VisiLogic.

    In U90, the  Modbus function does the translation from   MI 1  to the Modbus register number     and     reverse

     

     

    DanT

     

     

  10. Hi;

    The UCR 5 and 8 Routers from Unitronics do not yet have any interface for Vision support for SMS messaging.

    Has anyone done SMS messaging for a Vision  thru the UCR Routers ( or the Routers they are based on).?

    There are some options within the Routers for SMS, but I have not been able to get them to work. I have tried several so far.

    Curious about what method works. ( Tried Protocol TCP  via SMS Gateway-Post- looks do-able, but missing something,   Email to SMS -  cumbersome to implement - no success)

    SMS can be done Manually, but this is within the router itself, that works.

     

    DanT

     

     

  11. Hi;

    I doubt that Unitronics will put TRAIC outputs in  t heir PLC's. All their designs are based on 24 VDC with some 12VDC units. - which makes then universally adaptable.

    The Remote I/O    Ethernet based,  URB-TCP  do have  AC Solid State  Output modules.

    Other option is  PNP outputs from the PLC and I/O   and use solid state relays.   ( more costs effective to replace a blown relay than a whole PLC.)

     

    DanT

     

     

  12. Hi;

    The Data from the Scale is being sent as an ASCII String  ( Not an actual Number  - ML or MI)

    In Info Mode  in the PLC, look at the Serial Port  Monitor  and see what the data being received there looks like.

    Receive  as  a   Stream     of     Vector Length 3  ( convert 2 Bytes to Linked Element(MI) )  with the CR,LF as the End of Text(EOF)( Length 2)

    Make sure the 4th MI is set to   0x00   NULL      >>     12  34 56  0x00      (Note:  You can look at the MI's On Line  in HEX Format - easy read for ASCII Data)

    THEN  convert the ACSII String   to an ML  in the ladder. >>   Strings     ASCII to Num

    ( Have an ASCII Table handy ! )

    DanT   

     

     

    • Like 1
  13. Hi;

     

    For the HMI 

        Under Text,   List of texts

               Create an Indexed List and call them by the      FaultCode  ( int 32)  ( your switch case index )  in the program

                    ( FaultCode  being what ever name you choose )

     

    In the Ladder  -  Use the    Compare =    to Set the  Fault Code   to the Fault number  

    or  -- this one is neet --

    Under Solution explorer   use the   Switch Case   and set up the   FaultCode    to the List of Texts 

                    There is a lot of flexibility in this function   - Fixed  compares and ranges    with   Options for Actions

    Example  :    Case ID 1 ,  Name Case 1, Comparison Type - Value , From   #1 ( a Constant),  To   (Blank) ,   Action  (Store Tag)    , Tag (FaultCode)   Store into Tag ( #1   a Constant)

     

    DanT

     

  14. Hi;

     

    Under Screens,  Numeric Elements, there are 2   IP Address  Options

                IP Address Edit   -- you can select which IP Address to  view and edit   ( IP Address Type)

               IP Settings Edit  --   Panel, CPU, DNS  -- View and edit

    These are all editable from the screen

     

       In the Ladder  - Strings   --  IP to String    and        String to IP    ( no info in Help for explanations)

           IP to String       allows an  ASCII   Variable

         ASCII to String  -- does not allow setting a Panel IP  -- from what I can see.

     

        ( Don't have  UniStream to play with  right now  - else I would test them out )

     

    DanT

     

     

     

          

  15. Hi;

    Do not know of a ready made example, BUT :

    Help - Examples-  V900 - Projects - Communications - EXF-RC15 -   2 examples there, modify and rename the IN and OUT Subroutines and add a 2nd set for the 2nd RC15.  

                                                Modify the MB's and MI's etc. for the 2nd RC15

        locate how to change the CANBUS  address for the 2nd module

     

    DanT

  16. Hi;

     

    Comment for future :

    from the comment  in 1st post :  The only thing I haven’t tried, is swapping out the plug in I/O board with one of the other known working units, to find out if it's the I/O or the PLC itself. I am nervous about trying this as I can’t afford to have a second one fail if something has caused a component to blow. 

    The I/O board Analog Inputs and Outputs are factory calibrated and data stored on the Main Board.

    Swapping I/O board with another unit's I/O board will mess up that calibration, and Analogs May Not Work at all.

     

    DantT

×
×