  1. Hi;

    Where are you using these coils as coils else where   in your program?  

    If you use a coil  as a coil say 3 times in a program, only the last state of  the coil is  valid at the end of the program scan.

    Remember a PLC Scan starts at the top and ends at the bottom.

    Coils  MB 312,313,314 and 317    must have other factors controlling them.

    Can you post a copy of your program.

     

    DanT

  2. Hi Jesse;

    I looked at your program again and began to edit a few things.

    You have the PLC name set as an Indirect address  MI  0    -- as set up   -- the name of the PLC is a NULL ( No Name)

    You are trying to use a MI  Integer as the name, this will not work - I found the screen where you assign the PLC Name - COMMS

    The name should be an ASCII   String, and if you tried to write a name here(MI 0), you will overwrite MI1,MI2, etc. or Invalid ACSII Characters

     Even if the Name is to be a number, the  number is entered as an ASCII String   --     Modify your COMM HMI Screen to enter the PLC Name 

    Store the PLC Name some where else   - in your program I chose  MI 500 

    Maybe for testing, enter a  the PLC Name as a Direct String      like  V130TR6

    The PLC Name acts like a password to access the PLC

    Look up    PLC Name     in Help

      Attached  are my revisions -- to the program --  my revisions are in   Startup Net  and  COMMS   HMI

     

    Just as a note:      MI's  can be used to store and work with   Integer Numbers,  and also  store and work with ASCII Chars

                                          When you use MI's to store ACSII Chars, change the view from   DEC to HEX    and have an ACSII Table  handy 

     

    DanT

    622564519_FilterLevelDisplay_Dan0429A.vlp

  3. Hi Jesse;

     

    I downloaded your program and have looked it over.

    A few Comments:

       1   You have many nets that have multiple logical statements in them

                       Break them out into  individual nets,  Look at the STL  Quick view.

                      Unitronics ladder processing prefers 1 logical statement  to produce 1 finite output from the net, not many logical statements and a confused final output.

                        ( I have seen cases where multiple statements in the same net gave the WRONG output desired, breaking them out into individual nets cleared the problem)

                     Unitronics has no limits for the number of nets in a subroutine.

      2.  In the     !Home   Routine,    Break  up Net 1  into 2   separate nets

                                    Store and MB 31 in one  Net

                                    Com setup in another Net

    3.   In  the       !Home Routine ,    Break up  Net 2  into 2 separate nets,   Place the     Modbus IP Scan     in its own net  BEFORE calling the Main Subroutine.

                    The way you have it placed is that it will be processed AFTER the Main Subroutine has been processed.

     4.   In the    Admin Password    Subroutine   Break into 2 separate Nets                     Change the     --|  SB54 |----     to a      ---| P |---   Leading edge one shot pulse

    5.   In the   Main Subroutine   -- Break all those subroutine calls in Net 1  into individual nets, they will still get called in sequence.

    6.  Unitronics has defaults for setting up the Ethernet Sockets.  You can modify them as needed, or restate them in the net to avoid ambiguity ( I do this in my programs)

    7.  If you want your SCADA to pick up specific data, and it is spread out over different  MI's,   regroup them together in 1 area to make the Modbus calls easier.

             ( if you cannot regroup them , then use a   STORE   to send them to a grouping area)

    Doing these will help you troubleshoot your connection issues.

     

    DanT

     

     

     

  4. Hi;

    The UniStream Series has the  ability to do a Virtual HMI.

    The Models with the HMI  ( USP, US5,US7,US10 ) can be accessed by a  VNC Connection - the PLC's have a VNC Server built in - Just activate it.

    The USC-xx-xxx   Models, the HMI is Virtual  - you create the HMI as it it is actually there, then activate the internal VNC Server to make it available.

     Use a VNC Viewer Program ( They are normally Free downloads from various developers)  and view the Operator Screen remotely.

      There are 2 Modes for VNC  -- Read Only -- Can View the screen , but not do anything on it,   or  Read-Write - View and Control as if you were at the screen in person

    The VNC Server can be set up with Passwords.

    DanT

    • Like 1
  5. Hi ;

    First you need a  reliable time base.

    The only reliable time base  will be the   100ms  pulse   so use it to turn a MB on and off every 100ms   = 5 Hz

    Scan time is not reliable as it can vary  from place  processor activity, it may be faster, but not steady.

    You could look at the Interrupt routines -- 1.25mS  and 2.5mS   they have to be very short to be effective and not slow down the PLC processing.

                                            There are programs in Example to show how to use them.  You will have to test and experiment.

     

    Move over to a Vision PLC that has the PTO  Outputs already available.

     

    DanT

     

     

     

     

     

     

     

  6. Hi;

    You will  need to set up the RS232 Com Port

    You can use the FB Protocol  Function blocks to send the data string.

    Under Help, go to Examples, and then to Communications and look at the examples under FB Protocol.

         the Example      V130_Send_number_and_string          illustrates how to do this.

    In Help - search  fb s library  and then Communications Protocol

    Experiment, post your code  with your questions.

     

    DanT

     

     

     

     

  7. Hi Ratsept;

     

    Download the UniStream Examples Zip file from the UniStream Downloads section.

    There are Modbus examples under Communications.

    The Modbus is set up under protocols and creates a Struct  in Global Variables that has data in there about how the 

    communications are working - Attempts, successes, fails, and status codes, and more.

    Optional -  Post your Code  and we can review it.

     

    DanT

     

    • Like 1
  8. Hi Willis;

     

    The JZ20-J-T20HS  has 2  NPN  HSO   -- Review the Spec Sheet and the Installation guide

    There are a few example programs in the Help-Examples-Motion  of the U90 ladder Program.   Review these.

    On the Drive, the DIR   will determine the direction the stepper will turn ( on or OFF.  the PUL  will move the stepper ( High Speed output).

    For proper wiring, you will need the PDF  data sheet for the driver  to review the interface and  determine wiring.

    Create a schematic of the interface, and we can review and guide.

    DanT

     

  9. Hi Ash;

    Get the serial Numbers from the PLC's   and contact Unitronics Support with the model number and serial number and they may be able to

    give you the MAC  Addresses of the PLC's.

    From there use an IP Sniffer program that looks at the MAC Addresses and provides the IP Addresses.

    Perhaps  Unitronics Support can help you via a remote session.

    Once that, look and see if you can   Upload the program from the PLC's.

    Try to contact the vendor for the program also.

     

    DanT

  10. Hi Ash;

    Do these have a Unitronics USL  Display attached to them or are they "blind"?  

           If a USL Display, can you get into UniApps? ( Press touch screen Upper Right Corner area. )

    Do you have a VNC Connection to them?  This will have the Panel IP  in the Setup

    Were these done inhouse or outside vendor?  If outside vendor, contact them.

    Contact Unitronics Support and give them the Model number and the Serial Number. They may be able to provide the MAC address.

    Another thing:  Is this PLC a Modbus Slave to another device?  it will have the USC panel address there.

    DanT

  11. Hi;

    Tested this out, has the same issue on my test PLC  this morning.

    Found out I had an IP Address Conflict.  (There is another PLC plugged into the network with the same IP ( IP address is in a range we use to "Play/Test"  PLC's) )

    Disconnect the PLC from the network and ping the IP Address the PLC was on.  Getting the returns? - got a conflict.

    Test ping another IP Address, look for a free one.

    Manually change the IP address in the PLC via Info mode( be sure to apply) and   then plug the PLC into the network and ping the new address.

     If good, then try the PLC Connect again. If good, then figure out who the other IP Address belongs to and  decide which one gets the permanent change.

     

    DanT

     

     

     

  12. Hi;

    Unitronics PLC's do not support  Thermistors.

    Unitronics PLC's with temperature inputs support   Thermocouples or  100ohm RTD   or 1 kohm RTD ( IO Module)

    You can refer to the installation sheet that came with the PLC or look on line at Unitronicsplc.com , Technical support and tech documents

    for the model you have.

     

    You can look up on the internet  for a Thermistor interface to a 0-10V  analog input. 

    The calibaration will be up to you to figure out - do the math.

    Note that analog inputs on models without temperature input are 10 bit ( 0-1023)

     and on models with Temperature inputs the analog resolution is 14 bit ( 0-16767)

    DanT

     

  13. Hi;

     

    One observation:

       Many different logical statements inside  each net.  PLC Compiler has to " chew through " a lot to get 1 final result  of 2 or 3  different operations.

          ( look at the STL Statements   for these nets) 

          That one with 3 references to MB56  will cause problems   -( )-  and  2 x   -(P)-     Break it up.   The Leading edge pulses can get missed  in the current setup.

      Separate into  individual nets.  - The STL's are simpler to work on and  the result is simple - The plc  will process them easier.

     

      I have seen cases when having more than 1 logical  sequence in a net gives an un-expected wrong result. 

    Unitronics recommends 1 logical statement per net.

     

      

    DanT

     

  14. Hi Hasan;

    The Example program were created before the SAMBA was developed and the models used have more memory available.

    In these cases you can  re-assign the memory locations from the higher ranges to the ranges for the Samba within VisiLogic .

    Under Edit  there are a few real handy functions :

             Find Operand    -- see where an operand is used and how many times

            Replace Operand   --   to move an operand from 1 MB/MI   to another

    Open the example, review the  MB's, MI's  and move them to the SAMBA range, Save the program under an new name

         Then Under  View, Hardware config   change the hardware to the SMABA Model

       OR   Place the revised ladder into a subroutine and export the subroutine  and import the subroutine into the SAMBA Program

                  and deal with the warnings.   

              Also remember to check the Analog setups and redo manually in the SAMBA

     

    HMI's are more difficult to work with , they cannot be exported and imported into a SAMBA, so best to re-create them in the SMABA HMI.

    The SAMBA has a Limited Memory range for both Ladder and HMI.

    DanT

     

  15. Hi;

     

    The M91  and JAZZ Series PLC's have 2 Passwords that can be set.

          1 Password   BLOCKS   ALL   Communications to the PLC ( No download, no upload, no devices that need communications to operate)

                   When  this is set, then you have to know the password  to unlock  it.

          1  Password  allows communication, BUT does not allow UPLOAD  of the program unless you have the password.

          There is NO Backdoor to getting to the  program if these passwords are set

    Refer to Help  -- Project properties for the explanations.

    If the PLC was programmed by the machine manufacturer, then contact them. They had reasons to protect the PLC from being tampered with.

     

    DanT

  16. HI;

     

    Looking at the Data Stream, the clue is the    *  Character.  Try it as the ETX  or as STX

    Data Format appears stable - size and comma locations

    Bring in as  a string and the parse it to extract the data.

    You may also be able to extract the data on the fly as it is formatted already.

    Look at  Examples - Communications - FB Protocol -   V130 Receive 4 Numbers

    DanT

     

  17. Hi;

    Looking for a bit of experienced guidance for a customer in setting up the Ethernet/IP Parameters and structures  for using an Keyence IV2G30F  Module.

    Anyone set one up with a UnIStream PLC?   - Your experience?

    Have got the Module information for connecting to an A-B PLC, has some data there, 

     